Home » Public Forums » GMCnet » NON GMC - Electrical Question (For the on board electricians)
NON GMC - Electrical Question [message #311111] |
Wed, 30 November 2016 11:03 |
|
JShot
Messages: 485 Registered: October 2006 Location: NW Ohio
Karma: 0
|
Senior Member |
|
|
Three strings of LED lights. Each plugged into a separate outside, weather protected duplex outlet.
All three outlets are on the same circuit, and are activated by a wall switch inside the house.
When on, all strings light up normally. When off, all three strings still light up, but at about 30% of normal.
Opinions???
TIA,
John
John Shotwell
Ridgeville Corners, OH
78 Royale Center Kitchen
|
|
|
Re: NON GMC - Electrical Question [message #311112 is a reply to message #311111] |
Wed, 30 November 2016 11:14 |
Hal StClair
Messages: 971 Registered: March 2013 Location: Rio Rancho NM
Karma: -12
|
Senior Member |
|
|
Bad switch letting a small amount of current through. Might possibly have a wiring issue with a neutral loose somewhere and getting a back feed too.
Hal
"I enjoy talking to you. Your mind appeals to me. It resembles my own mind, except you happen to be insane."
1977 Royale 101348,
1977 Royale 101586, Diesel powered,
1974 Eagle Bus 45',w/slideout,
Rio Rancho, NM
|
|
|
|
Re: NON GMC - Electrical Question [message #311116 is a reply to message #311111] |
Wed, 30 November 2016 11:34 |
C Boyd
Messages: 2629 Registered: April 2006
Karma: 18
|
Senior Member |
|
|
RUN JOHN.... RUN...
JShot wrote on Wed, 30 November 2016 12:03Three strings of LED lights. Each plugged into a separate outside, weather protected duplex outlet.
All three outlets are on the same circuit, and are activated by a wall switch inside the house.
When on, all strings light up normally. When off, all three strings still light up, but at about 30% of normal.
Opinions???
TIA,
John
C. Boyd
76 Crestmont
East Tennessee
|
|
|
Re: NON GMC - Electrical Question [message #311118 is a reply to message #311111] |
Wed, 30 November 2016 12:44 |
|
SeanKidd
Messages: 747 Registered: June 2012 Location: Northern Neck Virginia
Karma: 4
|
Senior Member |
|
|
This is very common,most LEDs will operate at very low voltages, through capacitive discharge, inductive coupling from an adjacent circuit, or unbalanced neutral. This also occurs frequently on 3-Way circuits for the same reason...
Sean and Stephanie
73 Ex-CanyonLands 26' #317 "Oliver"
Hubler 1-Ton, Quad-Bags, Rear Disc, Reaction Arms, P.Huber TBs, 3.70:1 LSD Honda 6500 inverter gen.
Colonial Travelers
[Updated on: Wed, 30 November 2016 12:44] Report message to a moderator
|
|
|
|
|
|
|
Re: NON GMC - Electrical Question [message #311157 is a reply to message #311111] |
Thu, 01 December 2016 11:18 |
jhbridges
Messages: 8412 Registered: May 2011 Location: Braselton ga
Karma: -74
|
Senior Member |
|
|
Homer the Despot has them for $4.91. Cheap at twice that.
--johnny
Foolish Carriage, 76 26' Eleganza(?) with beaucoup mods and add - ons.
Braselton, Ga.
I forgive them all, save those who hurt the dogs. They must answer to me in hell
|
|
|
Re: NON GMC - Electrical Question [message #311183 is a reply to message #311126] |
Fri, 02 December 2016 10:07 |
TR 1
Messages: 348 Registered: August 2015 Location: DFW
Karma: -7
|
Senior Member |
|
|
JShot wrote on Wed, 30 November 2016 16:41Thanks for the ideas! I'll kill the circuit tomorrow and pull the switch and outlets to check their wiring. The house was built in 1971, and they ran 12-2 with ground to ALL of the duplex outlets (83 of them), BUT used ungrounded outlets. That's right - no ground hole, and the bare ground was just loose in the boxes.
When we moved in, I replaced all of the outlets with grounded ones, and put in all new switches. But I may have missed the outlets on the front porch
We'll see tomorrow.
Thanks again,
John
Built in 71, having an odd electrical issue and wired with 12awg wire? Make sure your house is not wired with aluminum wire... Was common around that time, and due to a myriad of factors is a fire hazard. If your house is wired with aluminum, you should very soon consider rewiring the house or there is a procedure to "re-terminate" the aluminum with copper...
Aluminum household wiring is a ticking time bomb...
Mark S. '73 Painted Desert,
Manny 1 Ton Front End,
Howell Injection,
Leigh Harrison 4bag and Rear Brakes,
Fort Worth, TX
|
|
|
Re: NON GMC - Electrical Question [message #311184 is a reply to message #311183] |
Fri, 02 December 2016 10:16 |
TR 1
Messages: 348 Registered: August 2015 Location: DFW
Karma: -7
|
Senior Member |
|
|
TR 1 wrote on Fri, 02 December 2016 10:07JShot wrote on Wed, 30 November 2016 16:41Thanks for the ideas! I'll kill the circuit tomorrow and pull the switch and outlets to check their wiring. The house was built in 1971, and they ran 12-2 with ground to ALL of the duplex outlets (83 of them), BUT used ungrounded outlets. That's right - no ground hole, and the bare ground was just loose in the boxes.
When we moved in, I replaced all of the outlets with grounded ones, and put in all new switches. But I may have missed the outlets on the front porch
We'll see tomorrow.
Thanks again,
John
Built in 71, having an odd electrical issue and wired with 12awg wire? Make sure your house is not wired with aluminum wire... Was common around that time, and due to a myriad of factors is a fire hazard. If your house is wired with aluminum, you should very soon consider rewiring the house or there is a procedure to "re-terminate" the aluminum with copper...
Aluminum household wiring is a ticking time bomb...
Significance of mentioning 12awg in my post above is that 12awg aluminum is needed to support a standard 15 amp circuit... This would normally be 14awg if using copper...
Mark S. '73 Painted Desert,
Manny 1 Ton Front End,
Howell Injection,
Leigh Harrison 4bag and Rear Brakes,
Fort Worth, TX
|
|
|
Re: NON GMC - Electrical Question [message #311188 is a reply to message #311111] |
Fri, 02 December 2016 11:00 |
jhbridges
Messages: 8412 Registered: May 2011 Location: Braselton ga
Karma: -74
|
Senior Member |
|
|
When she and I had our first house built, I saw what was going on in the subdivision, and took the electrician a 250' roll of copper 12/2 and ground. Two houses in the subdivision have burned, the others have all been rewired. Mine's going strong after 45 years, according to the current owner. Interesting trivia - the house was built using old bricks from the death house at Kilby Prison in Montgomery. More than one con 'rode the lightning' inside them.
--johnny
Foolish Carriage, 76 26' Eleganza(?) with beaucoup mods and add - ons.
Braselton, Ga.
I forgive them all, save those who hurt the dogs. They must answer to me in hell
|
|
|
|
Re: NON GMC - Electrical Question [message #311200 is a reply to message #311156] |
Fri, 02 December 2016 22:10 |
Ken Burton
Messages: 10030 Registered: January 2004 Location: Hebron, Indiana
Karma: 10
|
Senior Member |
|
|
Well there goes that idea.
Is the wall switch by chance switching the neutral side rather than the hot side of the circuit?
I do not see how the GFI could be causing your problem, but I have been wrong more than once.
You have an induced voltage or a leak somewhere. What would be interesting is to see what the voltage is at the receiptical while the lights are glowing. Also to see what happens to that voltage if you plug a normal 5, 25, or 40 watt incandescent lamp into the GFI.
Ken Burton - N9KB
76 Palm Beach
Hebron, Indiana
|
|
|
|
|
Re: NON GMC - Electrical Question [message #311203 is a reply to message #311202] |
Sat, 03 December 2016 06:22 |
tphipps
Messages: 3005 Registered: August 2004 Location: Spanish Fort, AL
Karma: 9
|
Senior Member |
|
|
John, Are you saying that you replaced all the outside outlets with GFI outlets? GFI outlet should be on the end of the string only. I did this once and it caused crazy electrical operation. Changing back to only one cured the problem.
Tom, MS II
2012 Phoenix Cruiser model 2552
KA4CSG
|
|
|
Re: NON GMC - Electrical Question [message #311257 is a reply to message #311126] |
Mon, 05 December 2016 08:39 |
stick miller
Messages: 1036 Registered: March 2010 Location: Americus, Georgia
Karma: 0
|
Senior Member |
|
|
JShot wrote on Wed, 30 November 2016 17:41Thanks for the ideas! I'll kill the circuit tomorrow and pull the switch and outlets to check their wiring. The house was built in 1971, and they ran 12-2 with ground to ALL of the duplex outlets (83 of them), BUT used ungrounded outlets. That's right - no ground hole, and the bare ground was just loose in the boxes.
When we moved in, I replaced all of the outlets with grounded ones, and put in all new switches. But I may have missed the outlets on the front porch
We'll see tomorrow.
Thanks again,
John
John - you're better off than I am. My house, built in 1910, had no grounded outlets when we moved in. After upgrading the service to 200A, that still left me with many unusable 2 hole plugs. I've replaced all the 2 holers with 3 holers, but nary a ground in the front part of the house.(Kitchen was completely rewired while the plaster was down). I guess we've ben lucky with no failures or problems in almost 13 years.
Stick Miller
'78 Royale - "White Trash" - she left me for another man
'76 Eleganza - "Cousin Eddie" Sold '84 Bluebird Wanderlodge - "Past Tents"
Americus, GA
|
|
|
Re: NON GMC - Electrical Question [message #311265 is a reply to message #311111] |
Mon, 05 December 2016 10:51 |
jhbridges
Messages: 8412 Registered: May 2011 Location: Braselton ga
Karma: -74
|
Senior Member |
|
|
Our original Georgia house, built in 1901 and razed fopr the highway several years ago, had tube and post wiring. Which, I was told, was still legal. But since it was groundless, and I didn't want uit under insulation in the attic, I replaced everything with 12-2/G and 14-2/G in the crawl space and put the grounds in for the plugholes.
--johnny
Foolish Carriage, 76 26' Eleganza(?) with beaucoup mods and add - ons.
Braselton, Ga.
I forgive them all, save those who hurt the dogs. They must answer to me in hell
|
|
|