Suburban SF-30 furnace [message #99472] Sun, 12 September 2010 17:36 Go to next message
carnutbill is currently offline  carnutbill   United States
Messages: 65
Registered: February 2004
Location: Rochester N.Y.
Karma: 0
Member
My 2 year old Suburban SF-30 gas furnace stop working, I have a full propane tanks & gas is getting to furnace. I have 2 20 pound tanks in the propane compartment. It worked once but now it runs for 20 seconds & shuts down. any suggestions? thanks bill

75 pb
Re: [GMCnet] Suburban SF-30 furnace [message #99476 is a reply to message #99472] Sun, 12 September 2010 18:20 Go to previous messageGo to next message
Bobby Gray is currently offline  Bobby Gray   United States
Messages: 3
Registered: January 2007
Karma: 0
Junior Member


My furnace would run for a given number of seconds and shut off regardless of
temperature. I replaced the thermostat and it works fine now. I think it was
cycling due to current flow through the contacts rather than temperature


Bobby & Vickie Gray
bvlgray@yahoo.com
706 877-2211 or 2214








--My 2 year old Suburban SF-30 ---

_______________________________________________
GMCnet mailing list
List Information and Subscription Options:
http://temp.gmcnet.org/cgi-bin/mailman/listinfo/gmclist



Bobby & Vickie Gray Brighton, TN 78 Kingsley
Re: Suburban SF-30 furnace [message #99478 is a reply to message #99472] Sun, 12 September 2010 18:35 Go to previous messageGo to next message
rwbmitiopt@comcast.net is currently offline  rwbmitiopt@comcast.net   United States
Messages: 189
Registered: April 2005
Karma: 0
Senior Member
Bill
My Suburban is obstinate after it's been sitting for a month or more. I think it may be that the propane has leaked down or lost it's kindling point (if that's possible). I usually run the stove burners for a few minutes and give it another try. Has worked every time so far. BTW my furnace is about 4 years.
JWID
Randall
carnutbill wrote on Sun, 12 September 2010 15:36

My 2 year old Suburban SF-30 gas furnace stop working, I have a full propane tanks & gas is getting to furnace. I have 2 20 pound tanks in the propane compartment. It worked once but now it runs for 20 seconds & shuts down. any suggestions? thanks bill

75 pb



Randall Burns
Sammamish WA
75 EX GB
Re: Suburban SF-30 furnace [message #99479 is a reply to message #99472] Sun, 12 September 2010 18:36 Go to previous messageGo to next message
zhagrieb is currently offline  zhagrieb   United States
Messages: 676
Registered: August 2009
Location: Portland Oregon
Karma: 0
Senior Member
Any chance some of your air vents are blocked causing the furnace to overtemp and shut down?

Glenn


Glenn Giere, Portland OR, K7GAG '73 "Moby the Motorhome" 26'
Re: Suburban SF-30 furnace [message #99482 is a reply to message #99479] Sun, 12 September 2010 19:12 Go to previous messageGo to next message
rwbmitiopt@comcast.net is currently offline  rwbmitiopt@comcast.net   United States
Messages: 189
Registered: April 2005
Karma: 0
Senior Member
Bill
For clarification: is the furnace lighting or is it just the fan running? In other words, is the fan running, not senseing heat, and shutting down. That is what I read into your original post and hence my above reply.
Randall

Glenn Giere wrote on Sun, 12 September 2010 16:36

Any chance some of your air vents are blocked causing the furnace to overtemp and shut down?

Glenn



Randall Burns
Sammamish WA
75 EX GB
Re: Suburban SF-30 furnace [message #99493 is a reply to message #99482] Sun, 12 September 2010 21:01 Go to previous messageGo to next message
carnutbill is currently offline  carnutbill   United States
Messages: 65
Registered: February 2004
Location: Rochester N.Y.
Karma: 0
Member
It sounds like the furnace purges, then does not light, then times out because it doesn't see fire & shuts down.
Do the new style propane tanks with safety valves have too little pressure? bill

75pb
Re: Suburban SF-30 furnace [message #99494 is a reply to message #99493] Sun, 12 September 2010 21:10 Go to previous messageGo to next message
WD0AFQ is currently offline  WD0AFQ   United States
Messages: 7111
Registered: November 2004
Location: Dexter, Mo.
Karma: 207
Senior Member
I had a similar problem with my 30 and it was the wire to the thermostat. Had to run new wires.
Dan


3 In Stainless Exhaust Headers One Ton All Discs/Reaction Arm 355 FD/Quad Bag/Alum Radiator Manny Tran/New eng. Holley EFI/10 Tire Air Monitoring System Solarized Coach/Upgraded Windows Satelite TV/On Demand Hot Water/3Way Refer
Re: Suburban SF-30 furnace [message #99495 is a reply to message #99493] Sun, 12 September 2010 21:23 Go to previous messageGo to next message
rwbmitiopt@comcast.net is currently offline  rwbmitiopt@comcast.net   United States
Messages: 189
Registered: April 2005
Karma: 0
Senior Member
Bill
I'm using the new 20# tanks in my coach with only the above mentioned issue.. Does the stove light? Are the furnace and stove on the same line?
Randall
carnutbill wrote on Sun, 12 September 2010 19:01

It sounds like the furnace purges, then does not light, then times out because it doesn't see fire & shuts down.
Do the new style propane tanks with safety valves have too little pressure? bill

75pb




Randall Burns
Sammamish WA
75 EX GB
Re: Suburban SF-30 furnace [message #99525 is a reply to message #99495] Mon, 13 September 2010 06:35 Go to previous messageGo to next message
Rodney Hamilton is currently offline  Rodney Hamilton   Canada
Messages: 24
Registered: August 2005
Karma: 0
Junior Member
I too have a SF-30 now 5 years old, on the second season I had to pull the unit to clean/adjust the ignitor/flame sensor. And it's time again to do it. I can tell because the unit won't start unless I restrict the air into the combustion chamber by partially covering the inlet outside the coach. The unit will start and run as long as I reduce the air flow... time to adjust the ignitor/flame sensor.

A real bugger to extract from under the sink. This time around I'm going to cut an access lid into the top of the furnace so that I can clean and adjust the unit in place.

rwbmitiopt wrote on Sun, 12 September 2010 22:23

Bill
I'm using the new 20# tanks in my coach with only the above mentioned issue.. Does the stove light? Are the furnace and stove on the same line?
Randall
carnutbill wrote on Sun, 12 September 2010 19:01

It sounds like the furnace purges, then does not light, then times out because it doesn't see fire & shuts down.
Do the new style propane tanks with safety valves have too little pressure? bill

75pb






Rodney Hamilton
Late 76 PB, 455
Montreal Canada
Re: [GMCnet] Suburban SF-30 furnace [message #99526 is a reply to message #99472] Mon, 13 September 2010 06:39 Go to previous messageGo to next message
Steven Ferguson is currently offline  Steven Ferguson   United States
Messages: 3447
Registered: May 2006
Karma: 0
Senior Member
Clean the contacts in the thermostat. Very fine sand paper works.

On Sun, Sep 12, 2010 at 3:36 PM, Bill Gagnier <carnutbill@msn.com> wrote:
>
>
> My 2 year old Suburban SF-30 gas furnace stop working, I have a full propane tanks & gas is getting to furnace. I have 2 20 pound tanks in the propane compartment. It worked once but now it runs for 20 seconds & shuts down.  any suggestions? thanks  bill
>
> 75 pb
> _______________________________________________
> GMCnet mailing list
> List Information and Subscription Options:
> http://temp.gmcnet.org/cgi-bin/mailman/listinfo/gmclist
>



--
Steve Ferguson
Sierra Vista, AZ
_______________________________________________
GMCnet mailing list
List Information and Subscription Options:
http://temp.gmcnet.org/cgi-bin/mailman/listinfo/gmclist

Re: Suburban SF-30 furnace [message #99585 is a reply to message #99525] Mon, 13 September 2010 12:06 Go to previous messageGo to next message
carnutbill is currently offline  carnutbill   United States
Messages: 65
Registered: February 2004
Location: Rochester N.Y.
Karma: 0
Member
What adjustments should I make? I have the unit out & connected on the bench & it still doesn't work. The flame lights for a second & then goes out. bill

75pb
Re: Suburban SF-30 furnace [message #99631 is a reply to message #99585] Mon, 13 September 2010 20:05 Go to previous message
mike miller   United States
Messages: 3576
Registered: February 2004
Location: Hillsboro, Oregon
Karma: 0
Senior Member
carnutbill wrote on Mon, 13 September 2010 10:06

... I have the unit out & connected on the bench & it still doesn't work. The flame lights for a second & then goes out.


Sounds like something in your "flame sensing curcuit."

The sensor is on the same assembly as the "sparker."

There is a manual on bdub's site for the correct part names Rolling Eyes and correct set up.


Mike Miller -- Hillsboro, OR -- on the Black list
(#2)`78 23' Birchaven Rear Bath -- (#3)`77 23' Birchaven Side Bath
More Sidekicks than GMC's and a late model Malibu called 'Boo' http://m000035.blogspot.com