circuit breaker terminology? [message #83176] |
Wed, 05 May 2010 12:47 |
fred v
Messages: 999 Registered: April 2006 Location: pensacola, fl.
Karma: 0
|
Senior Member |
|
|
i'm still looking for my breaker locally. i need a
QO230SWN
i've found a QO230CP at Lowes. it looks the same. i cannot find anyone who can tell me the difference.
i know a QO230GFI means a ground fault interuptor.
anyone able to help me?
thanks,
Fred V
'77 Royale RB 455
P'cola, Fl
|
|
|
Re: circuit breaker terminology? [message #83177 is a reply to message #83176] |
Wed, 05 May 2010 13:14 |
midlf
Messages: 2212 Registered: July 2007 Location: SE Wisc. (Palmyra)
Karma: 1
|
Senior Member |
|
|
fred v wrote on Wed, 05 May 2010 12:47 | i'm still looking for my breaker locally. i need a
QO230SWN
I've found a QO230CP at Lowes. it looks the same. i cannot find anyone who can tell me the difference.
i know a QO230GFI means a ground fault interrupter.
anyone able to help me?
thanks,
|
They are two different breakers. The QO230CP is just a common 2 pole 120/240volt 30amp breaker. The “CP” denotes bulk bar coded breakers.
The QO230SWN Circuit Breaker is listed as a Miniature Circuit Breaker , Switch Neutral, Plug-On, 30A, 2-Pole, 120VAC breaker. This is quite a different beast as it switches the neutral also. This must be part of a non-GMC upfitted coach as this is part of a generator switch-over system. This breaker lists for $90-$100. The Square D web page is:
http://www.schneider-electric.us/products-services/product-detail/?event=productDetail&partNumber=QO230SWN&countryCode=us
You will need the SWN breaker to replace a SWN breaker, the CP will not be the proper breaker.
Steve Southworth
1974 Glacier TZE064V100150 (for workin on)
1975 Transmode TZE365V100394 (parts & spares)
Palmyra WI
|
|
|
|
Re: [GMCnet] circuit breaker terminology? [message #83232 is a reply to message #83176] |
Wed, 05 May 2010 16:52 |
GMCWiperMan
Messages: 1248 Registered: December 2007
Karma: 1
|
Senior Member |
|
|
Fred,
In considering what to do about this, you must remember the RV grounding
rule: "Neutral must be tied to Ground at the Power Source and ONLY at the
Power Source." Since the Onan's ground is permanently tied to the GMC, if
you don't disconnect its neutral when you switch to Shore Power, you'll have
Neutral and Ground connected on board as well as at the Shore Power pole --
a No-No which WILL cause a Shore Power GFCI to trip.
Ken H.
On Wed, May 5, 2010 at 1:47 PM, fred veenschoten <fredntoni@cox.net> wrote:
>
>
> i'm still looking for my breaker locally. i need a
> QO230SWN
> i've found a QO230CP at Lowes. it looks the same. i cannot find anyone who
> can tell me the difference.
> i know a QO230GFI means a ground fault interuptor.
> anyone able to help me?
> thanks,
>
> --
> Fred V
> '77 Royale RB 455
> P'cola, Fl
> _______________________________________________
> GMCnet mailing list
> List Information and Subscription Options:
> http://temp.gmcnet.org/cgi-bin/mailman/listinfo/gmclist
>
_______________________________________________
GMCnet mailing list
List Information and Subscription Options:
http://temp.gmcnet.org/cgi-bin/mailman/listinfo/gmclist
|
|
|
Re: [GMCnet] circuit breaker terminology? [message #83235 is a reply to message #83176] |
Wed, 05 May 2010 17:16 |
Dave Mumert
Messages: 272 Registered: February 2004 Location: Olds, AB, Canada
Karma: 0
|
Senior Member |
|
|
Hi Fred
You are unlikely to find that breaker at any 'big box' type store.
Try an electrical supply or wholesaler
City Electric (850-453-5552) or Dixie Electrical (850-437-5300)
If one of these don't stock it they will certainly be able to get it.
Good Luck
Dave Mumert
> -----Original Message-----
> From: gmclist-bounces@temp.gmcnet.org [mailto:gmclist-
> bounces@temp.gmcnet.org] On Behalf Of fred veenschoten
> Sent: Wednesday, May 05, 2010 11:48 AM
> To: gmclist@temp.gmcnet.org
> Subject: [GMCnet] circuit breaker terminology?
>
>
>
> i'm still looking for my breaker locally. i need a QO230SWN i've found a
QO230CP
> at Lowes. it looks the same. i cannot find anyone who can tell me the
difference.
> i know a QO230GFI means a ground fault interuptor.
> anyone able to help me?
> thanks,
>
> --
> Fred V
> '77 Royale RB 455
> P'cola, Fl
> _______________________________________________
> GMCnet mailing list
> List Information and Subscription Options:
> http://temp.gmcnet.org/cgi-bin/mailman/listinfo/gmclist
_______________________________________________
GMCnet mailing list
List Information and Subscription Options:
http://temp.gmcnet.org/cgi-bin/mailman/listinfo/gmclist
|
|
|
Re: circuit breaker terminology? [message #83266 is a reply to message #83176] |
Wed, 05 May 2010 21:27 |
fred v
Messages: 999 Registered: April 2006 Location: pensacola, fl.
Karma: 0
|
Senior Member |
|
|
thanks for all the info. i found the right one on line for 20 bucks but i needed it by Thursday.
http://www.relectric.com/Store/Circuit-Breakers/QO230SWN
Ken, i already trip GFI's both at home and at RV parks that have them. it may be that i don't have the SWN in there now.
i'm going over to the coach tomorrow and remove the old one. the power went out and when i checked the breakers one of them sparked so i ran out and unplugged the power. we had to leave so i didn't have a chance to look at it further. oddly it is the left hand one that sparked. according to the drawing i have that would be the generator breaker.
Fred V
'77 Royale RB 455
P'cola, Fl
|
|
|
Re: [GMCnet] circuit breaker terminology? [message #83277 is a reply to message #83266] |
Wed, 05 May 2010 23:18 |
GMCWiperMan
Messages: 1248 Registered: December 2007
Karma: 1
|
Senior Member |
|
|
Fred,
Whatever is causing the GFCI's to trip, you need to fix it. Without proper
grounding, you run too great a risk of becoming THE ground circuit for 120
VAC. While I don't have a current problem with grounding, I've started
using an external GFCI every time I plug in.
Ken H.
On Wed, May 5, 2010 at 10:27 PM, fred veenschoten <fredntoni@cox.net> wrote:
>
>
> thanks for all the info. i found the right one on line for 20 bucks but i
> needed it by Thursday.
> http://www.relectric.com/Store/Circuit-Breakers/QO230SWN
>
> Ken, i already trip GFI's both at home and at RV parks that have them. it
> may be that i don't have the SWN in there now.
>
> i'm going over to the coach tomorrow and remove the old one. the power went
> out and when i checked the breakers one of them sparked so i ran out and
> unplugged the power. we had to leave so i didn't have a chance to look at it
> further. oddly it is the left hand one that sparked. according to the
> drawing i have that would be the generator breaker.
>
> --
> Fred V
> '77 Royale RB 455
> P'cola, Fl
> _______________________________________________
> GMCnet mailing list
> List Information and Subscription Options:
> http://temp.gmcnet.org/cgi-bin/mailman/listinfo/gmclist
>
_______________________________________________
GMCnet mailing list
List Information and Subscription Options:
http://temp.gmcnet.org/cgi-bin/mailman/listinfo/gmclist
|
|
|
Re: circuit breaker terminology? [message #83300 is a reply to message #83176] |
Thu, 06 May 2010 07:50 |
fred v
Messages: 999 Registered: April 2006 Location: pensacola, fl.
Karma: 0
|
Senior Member |
|
|
i noticed i had this problem at the first rally i went to at Chumuchla and tripped the GFCI. i started searching and found 2 faulty grounds in the 120 wiring but the GFI still tripped. i now know a new spot to look. i'll report back.
thanks,
Fred V
'77 Royale RB 455
P'cola, Fl
|
|
|
Re: circuit breaker terminology? [message #83324 is a reply to message #83266] |
Thu, 06 May 2010 10:00 |
pzerkel
Messages: 212 Registered: September 2007 Location: Salisbury, IL
Karma: 0
|
Senior Member |
|
|
I do work for an electrical supplier which is a Square D supplier. We do not stock but can get the QO230SWN. they are around $50 each.
Should I bring some to DuQuoin?
Paul Zerkel
'78 Eleganza II
Salisbury IL (near Springfield)
|
|
|
Re: circuit breaker terminology? [message #83352 is a reply to message #83176] |
Thu, 06 May 2010 13:30 |
fred v
Messages: 999 Registered: April 2006 Location: pensacola, fl.
Karma: 0
|
Senior Member |
|
|
i just got back from checking and the problem was the breakers were not making good contact with the buss bar and were arcing. i cleaned everything up and bent the clips in tighter and all is well.
learned something from all this. should i put some Nolox on the contact points?
Fred V
'77 Royale RB 455
P'cola, Fl
|
|
|
|
Re: [GMCnet] circuit breaker terminology? [message #83356 is a reply to message #83355] |
Thu, 06 May 2010 14:01 |
k2gkk
Messages: 4452 Registered: November 2009
Karma: -8
|
Senior Member |
|
|
Another product similar to No-Alox is Penetrox.
And there are others that basically contain
powdered aluminum in a conductive grease.
* Mac Macdonald *
* Oklahoma City *
** "Money Pit" **
* '76 ex - P.B. *
----------------------------------------
From: ken0henderson@gmail.com
Date: Thu, 6 May 2010 14:52:21 -0400
To: gmclist@temp.gmcnet.org
Subject: Re: [GMCnet] circuit breaker terminology?
I would.
Ken H.
On Thu, May 6, 2010 at 2:30 PM, fred veenschoten wrote:
i just got back from checking and the problem was the breakers were not
making good contact with the buss bar and were arcing. i cleaned everything
up and bent the clips in tighter and all is well.
learned something from all this. should i put some Nolox on the contact
points?
--
_______________________________________________
GMCnet mailing list
List Information and Subscription Options:
http://temp.gmcnet.org/cgi-bin/mailman/listinfo/gmclist
|
|
|