Re: House Electrical Panel [message #370531 is a reply to message #370527] |
Thu, 22 September 2022 08:25 |
JohnL455
Messages: 4447 Registered: October 2006 Location: Woodstock, IL
Karma:
|
Senior Member |
|
|
I’m confused as most Coachmen had 30A with see/saw breakers switch over.
If you have need for a new shore cord, buy a TT30 25’ extension and cut off the female end and dress into your panel and strain relief.
Neutral and Ground in the coach are NOT bonded and should have no continuity. Neutral and Ground should only be bonded at the source building’s MAIN panel only and never at any branch panels.
John Lebetski
Woodstock, IL
77 Eleganza II
|
|
|