> Overspeed will result in overvoltage, which will toast equipment if it's much over, and over frequency which will help toas electric motors.
Overspeed results in an over-frequency condition that is linearly proportional to the amount of overspeed but the excitation system has a limiting device - the thyristor - which puts an upper bound on excitation and thus an upper bound on output voltage. It is this device which prevents output voltage from soaring in a no-load situation but it also serves to limit maximum output voltage in any operational circumstance.
Many motors will tolerate an over-frequency condition but may draw increased current or deliver decreased speed due to flux saturation of their magnetic components. I have regularly operated 60Hz rated motors at 80Hz in CNC positioning applications but each motor design has differing magnetic characteristics so this statement cannot be extrapolated to the A/C compressor and fan.
Did the OP ever report back as to whether the A/C restarted after the short-cycle lockout timer expired?
—Jim