DUO THERM furnace limit switch [message #65081] |
Fri, 20 November 2009 16:29 |
vernonite
Messages: 5 Registered: June 2009 Location: United States
Karma:
|
Junior Member |
|
|
My Duo Therm furnace (1978) comes on and runs for about a minute and then flame stops, fan continues (forever) no more heat.
I removed the limit switch and tested it with thermometer prob taped to Therm-o-disc and blowing on it with a hair drier, it opens at about 209 degrees and closes at 179 degrees (specs say 200 off, 170 on, close enough).
When I tested the furnace with limit switch jumped it runs but gets very hot. When air from vents reached 160 degrees I got concerned and shut it down (what is normal temperature of vent air?).
The fan is working good, lots of air from the 3 vents. Why does it get so hot as to trip the limit switch? or does the limit switch open and close during normal heat cycle? If is does then I must have a control module problem as it never recycles unless I turn the thermostat off and on.
If the limit switch is only a safty feature then it seems I must be getting too much flame to cause the overheating. Is there some way to adjust the flame?