Onan generator not putting out power [message #363162] Wed, 31 March 2021 16:33 Go to next message
Hager is currently offline  Hager   United States
Messages: 19
Registered: December 2020
Location: Granite City Illinois
Karma: 2
Junior Member
I have a 6000 watt onan generator model number is 6.ONH.IR/9000F could be an E It was running fine putting out 119 to 120 volts shut it down came back 30 minutes later and no voltage. I have checked the breakers and plugged into ground power and everything works like it should, So the problem is with the generator

Hager and Sissy 1975 Eleganza #5 of that year Has a plaque on the glove box from GMC Mostly stock with Renogy charging system and a few changes to the interior Eagle rims and through the bumper hitch Granite City Illinois
[GMCnet] Re: Onan generator not putting out power [message #363164 is a reply to message #363162] Wed, 31 March 2021 16:55 Go to previous messageGo to next message
James Hupy is currently offline  James Hupy   United States
Messages: 6806
Registered: May 2010
Karma: -62
Senior Member
Did you have a load on the generator when you shut it off, and, did you
pull your finger off the "stop" switch before it completely stopped? If in
fact, you did, perhaps you toasted the bridge rectifier. Simple inexpensive
fix for that. Contact Jim K. and order a replacement. Simple modification
to the tangs, and you are good to go.
Jim Hupy
Salem, Oregon

On Wed, Mar 31, 2021, 2:33 PM Jim wrote:

> I have a 6000 watt onan generator model number is 6.ONH.IR/9000F could be
> an E It was running fine putting out 119 to 120 volts shut it down came
> back 30 minutes later and no voltage. I have checked the breakers and
> plugged into ground power and everything works like it should, So the
> problem
> is with the generator
> --
> Hager and Sissy
> 1975 Eleganza #5 of that year
> Has a plaque on the glove box from GMC
> Mostly stock with a few changes to the interior
> Eagle rims and through the bumper hitch
> Granite City Illinois
> _______________________________________________
> GMCnet mailing list
> Unsubscribe or Change List Options:
>
_______________________________________________
GMCnet mailing list
Unsubscribe or Change List Options:

[GMCnet] Re: Onan generator not putting out power [message #363170 is a reply to message #363164] Wed, 31 March 2021 21:59 Go to previous messageGo to next message
jimk is currently offline  jimk   United States
Messages: 6734
Registered: July 2006
Location: Belmont, CA
Karma: 9
Senior Member
We can get you full instruction on location and what to do with the bridge
rectifier.

On Wed, Mar 31, 2021 at 2:55 PM James Hupy wrote:

> Did you have a load on the generator when you shut it off, and, did you
> pull your finger off the "stop" switch before it completely stopped? If in
> fact, you did, perhaps you toasted the bridge rectifier. Simple inexpensive
> fix for that. Contact Jim K. and order a replacement. Simple modification
> to the tangs, and you are good to go.
> Jim Hupy
> Salem, Oregon
>
> On Wed, Mar 31, 2021, 2:33 PM Jim wrote:
>
>> I have a 6000 watt onan generator model number is 6.ONH.IR/9000F could
> be
>> an E It was running fine putting out 119 to 120 volts shut it down
> came
>> back 30 minutes later and no voltage. I have checked the breakers and
>> plugged into ground power and everything works like it should, So the
>> problem
>> is with the generator
>> --
>> Hager and Sissy
>> 1975 Eleganza #5 of that year
>> Has a plaque on the glove box from GMC
>> Mostly stock with a few changes to the interior
>> Eagle rims and through the bumper hitch
>> Granite City Illinois
>> _______________________________________________
>> GMCnet mailing list
>> Unsubscribe or Change List Options:
>>
> _______________________________________________
> GMCnet mailing list
> Unsubscribe or Change List Options:
>


--
Jim Kanomata
Applied/GMC, Newark,CA
jimk@appliedairfilters.com
http://www.gmcrvparts.com
1-800-752-7502
_______________________________________________
GMCnet mailing list
Unsubscribe or Change List Options:



Jim Kanomata
Applied/GMC
jimk@appliedairfilters.com
www.appliedgmc.com
1-800-752-7502
Re: [GMCnet] Re: Onan generator not putting out power [message #363171 is a reply to message #363170] Wed, 31 March 2021 23:48 Go to previous messageGo to next message
Melbo is currently offline  Melbo   United States
Messages: 144
Registered: August 2018
Location: Albuquerque NM
Karma: 0
Senior Member
What Jim and Jim said. Happened to me.

Melbo


Albuquerque NM Bus Conversion 1978 MCI 1973 GMC
Re: Onan generator not putting out power [message #363199 is a reply to message #363162] Sat, 03 April 2021 09:18 Go to previous messageGo to next message
TR 1 is currently offline  TR 1   United States
Messages: 348
Registered: August 2015
Location: DFW
Karma: -7
Senior Member
Hey, would anyone have a copy of those instructions handy? I bought a bridge rectifier from Jim back in 2017 as a spare to carry, and I realize now, I don't think I have the instructions on what needs to be adapted to use the new version in place of the original....

If it matters, I have a 4K Onan...


Mark S. '73 Painted Desert, Manny 1 Ton Front End, Howell Injection, Leigh Harrison 4bag and Rear Brakes, Fort Worth, TX
Re: Onan generator not putting out power [message #363200 is a reply to message #363162] Sat, 03 April 2021 11:00 Go to previous messageGo to next message
RF_Burns is currently offline  RF_Burns   Canada
Messages: 2277
Registered: June 2008
Location: S. Ontario, Canada
Karma: 3
Senior Member
Here is a link to photos of the OEM and mods to the replacement.

Two of the pins are labeled + (positive) and - (Negative). Orient the original and replacement rectifiers so those pins are in the same position. Note the ones that need to be twisted to match the original.

In this photo, the original (OEM) is on the left. A new one is in the center, and a new one modified with twisted pins is on the right.

You can buy this from any electronic distributor for about $2.50 each. I'm kinda partial to DigiKey because of the fast & inexpensive shipping. Get one rated at 25 Amps and 1000 volts. The high voltage rating may save the replacement next time the generator is shut down under load.

http://www.gmcmhphotos.com/photos/onan/p17103.html


Bruce Hislop
ON Canada
77PB, 455 Dick P. rebuilt, DynamicEFI EBL EFI & ESC.
1 ton front end
http://www.gmcmhphotos.com/photos/showphoto.php?photo=29001
My Staff says I never listen to them, or something like that
[GMCnet] Re: Onan generator not putting out power [message #363201 is a reply to message #363200] Sat, 03 April 2021 11:15 Go to previous messageGo to next message
jimk is currently offline  jimk   United States
Messages: 6734
Registered: July 2006
Location: Belmont, CA
Karma: 9
Senior Member
Mark,
We can send over the instruction on where the Bridge Rectifier is located
and how to modify the connectors.
Trusting the terminals is ok , but it is not that easy as the legs normally
do not line up.

On Sat, Apr 3, 2021 at 9:00 AM Bruce Hislop wrote:

> Here is a link to photos of the OEM and mods to the replacement.
>
> Two of the pins are labeled + (positive) and - (Negative). Orient the
> original and replacement rectifiers so those pins are in the same position.
> Note the ones that need to be twisted to match the original.
>
> In this photo, the original (OEM) is on the left. A new one is in the
> center, and a new one modified with twisted pins is on the right.
>
> You can buy this from any electronic distributor for about $2.50 each.
> I'm kinda partial to DigiKey because of the fast & inexpensive shipping. Get
> one rated at 25 Amps and 1000 volts. The high voltage rating may save the
> replacement next time the generator is shut down under load.
>
> http://www.gmcmhphotos.com/photos/onan/p17103.html
>
> --
> Bruce Hislop
> ON Canada
> 77PB, 455 Dick P. rebuilt, DynamicEFI EBL EFI & ESC.1 ton front end
> http://www.gmcmhphotos.com/photos/showphoto.php?photo=29001
> My Staff says I never listen to them, or something like that
> _______________________________________________
> GMCnet mailing list
> Unsubscribe or Change List Options:
>


--
Jim Kanomata
Applied/GMC, Newark,CA
jimk@appliedairfilters.com
http://www.gmcrvparts.com
1-800-752-7502
_______________________________________________
GMCnet mailing list
Unsubscribe or Change List Options:



Jim Kanomata
Applied/GMC
jimk@appliedairfilters.com
www.appliedgmc.com
1-800-752-7502
Re: Onan generator not putting out power [message #363234 is a reply to message #363162] Mon, 05 April 2021 11:06 Go to previous message
jhbridges is currently offline  jhbridges   United States
Messages: 8412
Registered: May 2011
Location: Braselton ga
Karma: -74
Senior Member
In lieu of twisting the pins you can make up four short wires, each with a female spade connector on obne end and a male on the other.

--johnny


Foolish Carriage, 76 26' Eleganza(?) with beaucoup mods and add - ons. Braselton, Ga. I forgive them all, save those who hurt the dogs. They must answer to me in hell