Whats better....plugging into a 50amp outlet with an adaptor to 30amps or plugging into the 30amp outlet directly with a 30amp coach.

Curious to see what people hsve found if the 50amp with 30 adapter is better or 30amp direct puts out better power at sites.


Rich Mondor, Brockville, ON 77 Hughes 2600
Re: Plugging in to shore power [message #351376 is a reply to message #351375] Mon, 13 January 2020 07:33 Go to previous messageGo to next message
RF_Burns is currently offline  RF_Burns   Canada
Messages: 2277
Registered: June 2008
Location: S. Ontario, Canada
Karma: 3
Senior Member
Rich,
A 50Amp service is 240 VAC (two 120VAC legs to neutral). A 50Amp to 30 Amp adapter connects the 30 Amp cable to one of the 120V legs.

You could actually draw 50 Amps from this, but you are limited to 30 Amps in your panel by the main breaker.

The post 30 Amp outlet is 120VAC with a 30 Amp breaker at the post.

My opinion is the fewer connections the better, so if you have a 30 amp cord and there is a 30 amp outlet at the post, use the 30 Amp outlet. The other consideration is the 50 Amp adapter is usually a dog-bone cable which leaves the 30 Amp cable connector hanging outside in the weather. When plugged directly into a 30 amp outlet your cable connector is usually protected from weather under a hood.

Just mt 2 cents.


Bruce Hislop
ON Canada
77PB, 455 Dick P. rebuilt, DynamicEFI EBL EFI & ESC.
1 ton front end
http://www.gmcmhphotos.com/photos/showphoto.php?photo=29001
My Staff says I never listen to them, or something like that
Re: Plugging in to shore power [message #351377 is a reply to message #351375] Mon, 13 January 2020 09:15 Go to previous messageGo to next message
Ken Burton is currently offline  Ken Burton   United States
Messages: 10030
Registered: January 2004
Location: Hebron, Indiana
Karma: 10
Senior Member
Same same. The pedestal will supply up to 30 amps at 120 volts maximum no matter what you plug into it.

I prefer 240 volt at 50 amp because most places have this service these days and the cable will have 1/2 of the total current draw across any of the conductors for the same load. If I am forced to use a 30 amp pedestal then I simply add an adapter to the cable.


Ken Burton - N9KB
76 Palm Beach
Hebron, Indiana
Re: Plugging in to shore power [message #351378 is a reply to message #351375] Mon, 13 January 2020 10:24 Go to previous messageGo to next message
6cuda6 is currently offline  6cuda6   Canada
Messages: 975
Registered: June 2019
Karma: -6
Senior Member
I get what you guys are saying....thanks it makes sense.

Rich Mondor, Brockville, ON 77 Hughes 2600
Re: Plugging in to shore power [message #351379 is a reply to message #351378] Mon, 13 January 2020 11:36 Go to previous messageGo to next message
mghamms is currently offline  mghamms   United States
Messages: 466
Registered: March 2016
Location: Ware, Massachusetts
Karma: 2
Senior Member
the 30 amp plug gives 30 amps at 120 volts.
The 50 amp plug gives 50 amps on each leg so 100 amps at 120 volts.


1977 Kingsley 455 as stock as it gets except lots of Ragusa parts
Re: Plugging in to shore power [message #351381 is a reply to message #351375] Tue, 14 January 2020 08:28 Go to previous messageGo to next message
JohnL455 is currently offline  JohnL455   United States
Messages: 4447
Registered: October 2006
Location: Woodstock, IL
Karma: 12
Senior Member
Technically the 50 to 30A adaptor is not code. (14-50 to TT-30)
The post breaker is over sized for protecting the 30A cord set.


John Lebetski
Woodstock, IL
77 Eleganza II
Re: Plugging in to shore power [message #351385 is a reply to message #351379] Tue, 14 January 2020 19:30 Go to previous messageGo to next message
Bullitthead is currently offline  Bullitthead   United States
Messages: 1411
Registered: November 2013
Karma: 5
Senior Member
No 100 amps from the 50 amp circuit...25 amps on each power leg to neutral at 120 volts and 50 amps between both power legs at 240 volts.

Terry Kelpien ASE Master Technician 73 Glacier 260 Smithfield, Va.
Re: Plugging in to shore power [message #351386 is a reply to message #351385] Tue, 14 January 2020 20:45 Go to previous messageGo to next message
Hal StClair   United States
Messages: 971
Registered: March 2013
Location: Rio Rancho NM
Karma: -12
Senior Member
It's 50 amps per leg, a 2 pole 50 amp over currant devise. You can call it 100 amps but it's really 50 amps @ 240 volts. If you tried to pull 100 amps @ 120 volts you'd put twice the amps on the grounded conductor (neutral) that it is rated for. If you had a 2 pole 25 amp breaker, I'd give you the 50 amp total but again the same conditions applying to the neutral.
Hal


"I enjoy talking to you. Your mind appeals to me. It resembles my own mind, except you happen to be insane." 1977 Royale 101348, 1977 Royale 101586, Diesel powered, 1974 Eagle Bus 45',w/slideout, Rio Rancho, NM
Re: Plugging in to shore power [message #351388 is a reply to message #351386] Wed, 15 January 2020 06:38 Go to previous messageGo to next message
Ken Burton is currently offline  Ken Burton   United States
Messages: 10030
Registered: January 2004
Location: Hebron, Indiana
Karma: 10
Senior Member
Hal, I will enter the fray here.

The current on the neutral conductor will be the difference of the two hot conductors, not the sum. So if you had 25 amps on each of the hot conductors, the current on the neutral would be ZERO amps. If you had 25 on one and 20 on the other, then the current on the neutral would be 5 amps.

Respectively,

Ken B.


Ken Burton - N9KB
76 Palm Beach
Hebron, Indiana
Re: Plugging in to shore power [message #351389 is a reply to message #351375] Wed, 15 January 2020 08:14 Go to previous messageGo to next message
JohnL455 is currently offline  JohnL455   United States
Messages: 4447
Registered: October 2006
Location: Woodstock, IL
Karma: 12
Senior Member
Very true Ken B. But to be even pickier, GMC upfit coaches usually have a 40A dual pole main breaker at the coach box. When on Onan, the full combined L1 and L2 is carried by the neutral, but the 50A Onan breaker protects the cord set which was not designed for 80A on the neutral. So they thought it through

John Lebetski
Woodstock, IL
77 Eleganza II
Re: Plugging in to shore power [message #351390 is a reply to message #351389] Wed, 15 January 2020 09:40 Go to previous messageGo to next message
Ken Burton is currently offline  Ken Burton   United States
Messages: 10030
Registered: January 2004
Location: Hebron, Indiana
Karma: 10
Senior Member
You are correct. I thought were were talking feeding the coach with 240 volt shore power vs. 30 amp 120 volt shore power.

Ken Burton - N9KB
76 Palm Beach
Hebron, Indiana
Re: Plugging in to shore power [message #351391 is a reply to message #351375] Wed, 15 January 2020 09:50 Go to previous messageGo to next message
JohnL455 is currently offline  JohnL455   United States
Messages: 4447
Registered: October 2006
Location: Woodstock, IL
Karma: 12
Senior Member
We were. But to truly understand the reasons "why" , you really need a full understanding of the system. I assume he has a TT-30 non GMC upfit system. So-- if you have an 14-50P to TT-30R adapter at the shore post, you have the potential of overheating the TT-30 cord set, should a fault occur.

John Lebetski
Woodstock, IL
77 Eleganza II

[Updated on: Wed, 15 January 2020 09:51]

Report message to a moderator

Re: Plugging in to shore power [message #351392 is a reply to message #351391] Wed, 15 January 2020 10:59 Go to previous messageGo to next message
Bill Van Vlack is currently offline  Bill Van Vlack   United States
Messages: 419
Registered: September 2015
Location: Guemes Island, Washington
Karma: 14
Senior Member
Here is Blue Sea's explanation and diagram of neutral current on a 220/110v electrical system... As Ken Burton points out above, the load on the neutral is the imbalance of the load on each leg, so, for L1 at 15A load and L2 at 20A load the neutral load is 20-25=5 Amps.

Bill Van Vlack '76 Royale; Guemes Island, Washington; Twin bed, full (DS) side bath, Brazilian Redwood counter and settee tops,455, 6KW generator; new owner a/o mid November 2015.
Re: Plugging in to shore power [message #351393 is a reply to message #351388] Wed, 15 January 2020 18:33 Go to previous messageGo to next message
Hal StClair   United States
Messages: 971
Registered: March 2013
Location: Rio Rancho NM
Karma: -12
Senior Member
Ken Burton wrote on Wed, 15 January 2020 05:38
Hal, I will enter the fray here.

The current on the neutral conductor will be the difference of the two hot conductors, not the sum. So if you had 25 amps on each of the hot conductors, the current on the neutral would be ZERO amps. If you had 25 on one and 20 on the other, then the current on the neutral would be 5 amps.

Respectively,

Ken B.
True only if they are on different phases. When people start using 50/30 adapters loads imposed on the neutral can get out of wack depending on how the rest of the system is wired.
Hal


"I enjoy talking to you. Your mind appeals to me. It resembles my own mind, except you happen to be insane." 1977 Royale 101348, 1977 Royale 101586, Diesel powered, 1974 Eagle Bus 45',w/slideout, Rio Rancho, NM
Re: Plugging in to shore power [message #351394 is a reply to message #351375] Wed, 15 January 2020 19:37 Go to previous messageGo to next message
C Boyd is currently offline  C Boyd   United States
Messages: 2629
Registered: April 2006
Karma: 18
Senior Member
Sir, I prefer to plug our 30 amp Crestmont in a 30 amp outlet while I prefer to plug our 50 amp Eleganza II in a 50 amp outlet.





6cuda6 wrote on Mon, 13 January 2020 08:18
Whats better....plugging into a 50amp outlet with an adaptor to 30amps or plugging into the 30amp outlet directly with a 30amp coach.

Curious to see what people hsve found if the 50amp with 30 adapter is better or 30amp direct puts out better power at sites.


C. Boyd
76 Crestmont
East Tennessee
Re: Plugging in to shore power [message #351404 is a reply to message #351394] Fri, 17 January 2020 09:17 Go to previous messageGo to next message
Melbo is currently offline  Melbo   United States
Messages: 144
Registered: August 2018
Location: Albuquerque NM
Karma: 0
Senior Member
Isn't electricity fun?

If properly wired it should be as Ken says.

If not done properly you could end up with what Hal says.

Most of the "newer" pedestals seem to be wired correctly and I personally have not had issues. In older parks or Mexico I never trust them and typically check with a meter before connecting. If I get zero volts across the two hots on a 50 amp receptacle and 120 volts on each leg to ground I severely limit my electrical use just to be safe.

Just My Way.

HTH

Melbo


Albuquerque NM Bus Conversion 1978 MCI 1973 GMC
Re: Plugging in to shore power [message #351405 is a reply to message #351375] Fri, 17 January 2020 09:33 Go to previous messageGo to next message
JohnL455 is currently offline  JohnL455   United States
Messages: 4447
Registered: October 2006
Location: Woodstock, IL
Karma: 12
Senior Member
Besides all the other reasons listed, the more adaptors you add, the more Voltage drop you get, if the connectors are warm, you are losing Voltage. At some point it's like Clark Griswold in Christmas Vacation

John Lebetski
Woodstock, IL
77 Eleganza II

[Updated on: Fri, 17 January 2020 09:35]

Report message to a moderator

Re: Plugging in to shore power [message #351406 is a reply to message #351393] Fri, 17 January 2020 10:10 Go to previous messageGo to next message
Matt Colie is currently offline  Matt Colie   United States
Messages: 8547
Registered: March 2007
Location: S.E. Michigan
Karma: 7
Senior Member
Ken Burton wrote on Wed, 15 January 2020 05:38
Hal, I will enter the fray here.
The current on the neutral conductor will be the difference of the two hot conductors, not the sum. So if you had 25 amps on each of the hot conductors, the current on the neutral would be ZERO amps. If you had 25 on one and 20 on the other, then the current on the neutral would be 5 amps.
Respectively,
Ken B.
Hal StClair wrote on Wed, 15 January 2020 19:33
True only if they are on different phases. When people start using 50/30 adapters loads imposed on the neutral can get out of wack depending on how the rest of the system is wired.
Hal
Hal,

There is a severe nomenclature problem here.
For a 14-50 receptacle to be approved, the two hot (L1,L2) have to be the opposite ends of the same phase. This makes those two 180° out of phase. This is colloquially described in the trade (was mine once) as the "other side of the phase". Then we get to Y vs Delta vs Star (Multi-phase not seen shore-side).
If they were one leg on another phase, it would not be 240-120/120 because the legs would not not be 180° out, but leading or lagging by 120°. That is when you see numbers like 208, 168 & 86 Volts and now the guy that had to fix it has to try to find out what got done where and get the power back where the Chief wants it.

If someone were to connect a 14-50 as you suggest, yes, the neutral would be at risk. But, I do believe that in the USA and Canada most of that stuff is inspected. If a GMC owner does not carry a meter, he should get one at Hazard Fright for cheap. Most other 50 amp coaches that I have seen have safety systems or power protection devices that would warn the owners of this case.

Matt


Matt & Mary Colie - Chaumière -'73 Glacier 23 - Members GMCMI, GMCGL, GMCES
Electronically Controlled Quiet Engine Cooling Fan with OE Rear Drum Brakes with Applied Control Arms
SE Michigan - Near DTW - Twixt A2 and Detroit
Re: Plugging in to shore power [message #351407 is a reply to message #351404] Fri, 17 January 2020 10:12 Go to previous messageGo to next message
Ken Burton is currently offline  Ken Burton   United States
Messages: 10030
Registered: January 2004
Location: Hebron, Indiana
Karma: 10
Senior Member
One of the things I always do is check the connector(s) with my hand to see if any are getting warm. I do this after 5 or 10 minutes of running the coach and again a hour or two later.

Where there is heat there is a poor connection or an undersized wire. I also keep a 3 light tester inside. I just leave it plugged in all the time. Usually in the kitchen plug.


Ken Burton - N9KB
76 Palm Beach
Hebron, Indiana
Re: Plugging in to shore power [message #351408 is a reply to message #351375] Fri, 17 January 2020 11:59 Go to previous messageGo to previous message
JohnL455 is currently offline  JohnL455   United States
Messages: 4447
Registered: October 2006
Location: Woodstock, IL
Karma: 12
Senior Member
Since Matt got into the nuts and bolts of 14-50, there is one more "odd" condition to be aware of. If the neutral has a poor connection, your Voltage on the lighter loaded leg can swing ABOVE the 125V mark. This is because the lack of neutral connections allows the one phase to reference the other approaching the 240V present.