plug into GFI outlet [message #332173] Wed, 16 May 2018 12:37 Go to next message
kstockwell is currently offline  kstockwell   United States
Messages: 367
Registered: May 2016
Location: Putney VT
Karma: 4
Senior Member
Last week while plugged in at home my GFI outlet in the garage popped at some point. I had been using my vacuum cleaner (not the GMC one). I plugged it in again and later I noticed the GFI outlet was buzzing, not super loud but pretty loud.

So, I plugged into my house outlet (non GFI). This GFI outlet is new, the whole line to the garage is new we didn't have one before.

I plugged in this morning, waited for it to start buzzing- maybe 5 minutes. Then I shut breakers off. It would change the pitch of the buzz. I got to the one labeled water heater (on my panel it's the upper right) and the buzzing stopped. So, now what do I do? The water heater was off, I have a wire coming from the breaker box to an normal switch that says water heater. It's always off, I use propane to heat my water.

It's like it's not grounding out, but it's sort of grounded? It sounded like this, but only when I was plugged in.

https://www.youtube.com/watch?v=Fw2MdV1X1iU

thanks
kelly


1978 Kingsley Putney VT

[Updated on: Wed, 16 May 2018 12:37]

Report message to a moderator

Re: plug into GFI outlet [message #332191 is a reply to message #332173] Wed, 16 May 2018 16:48 Go to previous messageGo to next message
Ken Burton is currently offline  Ken Burton   United States
Messages: 10030
Registered: January 2004
Location: Hebron, Indiana
Karma: 10
Senior Member
Turning off the circuit breaker to the water heater does NOT disconnect the neutral and ground to the water heater. It sounds like you have a short in the heating element between neutral and ground. Replace the heating element or disconnect the neutral going to the water heating element. Electric heating elements failures are very common.

Ken Burton - N9KB
76 Palm Beach
Hebron, Indiana
Re: plug into GFI outlet [message #332193 is a reply to message #332191] Wed, 16 May 2018 17:19 Go to previous messageGo to next message
kstockwell is currently offline  kstockwell   United States
Messages: 367
Registered: May 2016
Location: Putney VT
Karma: 4
Senior Member
Thank you for the info. I should be ok in the meantime if I don't use the water heater on electric and keep the breaker off?
Then when I can I'll change the element. I'm not sure were that is; but I'm sure the internet will help me. It's a newer water heater, not stock

kelly


1978 Kingsley Putney VT
Re: plug into GFI outlet [message #332220 is a reply to message #332193] Thu, 17 May 2018 07:45 Go to previous messageGo to next message
mghamms is currently offline  mghamms   United States
Messages: 466
Registered: March 2016
Location: Ware, Massachusetts
Karma: 2
Senior Member
Most gmc's have the ground and neutral connected in the breaker box.
There is also the possibility that they are connected elsewhere.
These connections are what will trip the gfi. Gfi just Checks for an unbalanced load between the hot and neutral.
If the neutral and ground are connected some power may be transferred from the neutral to the ground and trip the gfi.
Your gfi may be bad now because of this. Change to a new gfi and use your rv with a none gfi outlet should fix your short term problem.


1977 Kingsley 455 as stock as it gets except lots of Ragusa parts

[Updated on: Thu, 17 May 2018 07:46]

Report message to a moderator

Re: plug into GFI outlet [message #332223 is a reply to message #332220] Thu, 17 May 2018 08:08 Go to previous messageGo to next message
kstockwell is currently offline  kstockwell   United States
Messages: 367
Registered: May 2016
Location: Putney VT
Karma: 4
Senior Member
I did more investigation because I realized the IOTA converter was also plugged into this breaker and my batteries were low. Apparently the IOTA DLS45 is what's tripping the GFIC
If I plug it into another outlet in the coach (not the one next to the circuit breaker that also goes to the water heater) it quickly trips. When plugged into the outlet by the circuit breaker it makes the GFI outlet buzz like crazy and eventually trips.

I just did a search and found this.
http://www.everything-about-rving.com/when-my-rv-is-plugged-into-a-gfci-outlet-the-power-converter-is-tripping-the-gfci.html

anyone else have this happen? I'm still not sure my GFI outlet is not the issue. It's new but I had a hot tub on this circuit once with a GFI breaker. Between the GFI on the end of the hot tub plug, and the GFI circuit breaker it didn't work out, we ended up putting in a normal circuit breaker. I now have a normal circuit breaker and a GFI outlet. though other things don't seem to make it buzz or pop.

We leave for music camp tonight. We went a month ago; I'm pretty sure I plug into a GFI outlet there; so I'll see if it happens there. If so this is a new thing, if not my GFI outlet is crap

kelly


1978 Kingsley Putney VT
Re: [GMCnet] plug into GFI outlet [message #332224 is a reply to message #332220] Thu, 17 May 2018 09:07 Go to previous messageGo to next message
Ken Henderson is currently offline  Ken Henderson   United States
Messages: 8726
Registered: March 2004
Location: Americus, GA
Karma: 9
Senior Member
Mike, et al,

Any GMC which has the ground and neutral connected in its breaker box is
MISWIRED and DANGEROUS. That connection should be made ONLY in the shore
power box. To understand this requirement, read this:

https://docs.google.com/viewer?url=http%3A%2F%2Fwww.gmceast.com%2Ftechnical%2FBurton_Grounding_GMC_Motorhome.pdf
or
https://goo.gl/MW1lcP

Ken H.

On Thu, May 17, 2018 at 8:46 AM Mike Hamm wrote:

> Most gmc's have the ground and neutral connected in the breaker box.
> There is also the possibility that they are connected elsewhere.
> These connections ate what will trip the gfi. Gfi just Checks for an
> unbalanced load between the hot and neutral.
> If the neutral and ground are connected some power may be transferred from
> the neutral to the ground and trip the gfi.
> Your gfi may be bad now because of this. Change to a new gfi and use your
> rv with a none gfi outlet should fix your short term problem.
> --
> 1977 Kingsley 455 as stock as it gets except lots of Ragusa parts
>
>
_______________________________________________
GMCnet mailing list
Unsubscribe or Change List Options:
http://list.gmcnet.org/mailman/listinfo/gmclist_list.gmcnet.org



Ken Henderson
Americus, GA
www.gmcwipersetc.com
Large Wiring Diagrams
76 X-Birchaven
76 X-Palm Beach
Re: [GMCnet] plug into GFI outlet [message #332243 is a reply to message #332224] Thu, 17 May 2018 13:05 Go to previous messageGo to next message
kstockwell is currently offline  kstockwell   United States
Messages: 367
Registered: May 2016
Location: Putney VT
Karma: 4
Senior Member
this is what work printers are for. double sided, color ready to read this weekend

thank you



Ken Henderson wrote on Thu, 17 May 2018 10:07
Mike, et al,

Any GMC which has the ground and neutral connected in its breaker box is
MISWIRED and DANGEROUS. That connection should be made ONLY in the shore
power box. To understand this requirement, read this:

https://docs.google.com/viewer?url=http%3A%2F%2Fwww.gmceast.com%2Ftechnical%2FBurton_Grounding_GMC_Motorhome.pdf
or
https://goo.gl/MW1lcP

Ken H.

On Thu, May 17, 2018 at 8:46 AM Mike Hamm wrote:

> Most gmc's have the ground and neutral connected in the breaker box.
> There is also the possibility that they are connected elsewhere.
> These connections ate what will trip the gfi. Gfi just Checks for an
> unbalanced load between the hot and neutral.
> If the neutral and ground are connected some power may be transferred from
> the neutral to the ground and trip the gfi.
> Your gfi may be bad now because of this. Change to a new gfi and use your
> rv with a none gfi outlet should fix your short term problem.
> --
> 1977 Kingsley 455 as stock as it gets except lots of Ragusa parts
>
>
_______________________________________________
GMCnet mailing list
Unsubscribe or Change List Options:
http://list.gmcnet.org/mailman/listinfo/gmclist_list.gmcnet.org




1978 Kingsley Putney VT
Re: [GMCnet] plug into GFI outlet [message #332247 is a reply to message #332243] Thu, 17 May 2018 14:51 Go to previous messageGo to next message
sgltrac is currently offline  sgltrac   United States
Messages: 2797
Registered: April 2011
Karma: 1
Senior Member
I see in there that Ken B states that Paterson says to ground the dist to
the battery. If i remember correctly in my instructions that came with the
Paterson dist it said to ground it directly to the intake manifold.

Sully
77 eleganza 2
Bellevue

On Thu, May 17, 2018 at 11:33 AM kelly stockwell wrote:

> this is what work printers are for. double sided, color ready to read
> this weekend
>
> thank you
>
>
>
> Ken Henderson wrote on Thu, 17 May 2018 10:07
>> Mike, et al,
>>
>> Any GMC which has the ground and neutral connected in its breaker box is
>> MISWIRED and DANGEROUS. That connection should be made ONLY in the shore
>> power box. To understand this requirement, read this:
>>
>>
> https://docs.google.com/viewer?url=http%3A%2F%2Fwww.gmceast.com%2Ftechnical%2FBurton_Grounding_GMC_Motorhome.pdf
>> or
>> https://goo.gl/MW1lcP
>>
>> Ken H.
>>
>> On Thu, May 17, 2018 at 8:46 AM Mike Hamm wrote:
>>
>>> Most gmc's have the ground and neutral connected in the breaker box.
>>> There is also the possibility that they are connected elsewhere.
>>> These connections ate what will trip the gfi. Gfi just Checks for an
>>> unbalanced load between the hot and neutral.
>>> If the neutral and ground are connected some power may be transferred
> from
>>> the neutral to the ground and trip the gfi.
>>> Your gfi may be bad now because of this. Change to a new gfi and use
> your
>>> rv with a none gfi outlet should fix your short term problem.
>>> --
>>> 1977 Kingsley 455 as stock as it gets except lots of Ragusa parts
>>>
>>>
>> _______________________________________________
>> GMCnet mailing list
>> Unsubscribe or Change List Options:
>> http://list.gmcnet.org/mailman/listinfo/gmclist_list.gmcnet.org
>
>
> --
> 1978 Kingsley
> Putney VT
>
> _______________________________________________
> GMCnet mailing list
> Unsubscribe or Change List Options:
> http://list.gmcnet.org/mailman/listinfo/gmclist_list.gmcnet.org
>
_______________________________________________
GMCnet mailing list
Unsubscribe or Change List Options:
http://list.gmcnet.org/mailman/listinfo/gmclist_list.gmcnet.org



Sully 77 Royale basket case. Future motorhome land speed record holder(bucket list) Seattle, Wa.
Re: [GMCnet] plug into GFI outlet [message #332253 is a reply to message #332224] Thu, 17 May 2018 18:26 Go to previous messageGo to next message
mghamms is currently offline  mghamms   United States
Messages: 466
Registered: March 2016
Location: Ware, Massachusetts
Karma: 2
Senior Member
Ken Henderson wrote on Thu, 17 May 2018 09:07
Mike, et al,

Any GMC which has the ground and neutral connected in its breaker box is
MISWIRED and DANGEROUS. That connection should be made ONLY in the shore
power box. To understand this requirement, read this:

https://docs.google.com/viewer?url=http%3A%2F%2Fwww.gmceast.com%2Ftechnical%2FBurton_Grounding_GMC_Motorhome.pdf
or
https://goo.gl/MW1lcP

Ken H.

On Thu, May 17, 2018 at 8:46 AM Mike Hamm wrote:

> Most gmc's have the ground and neutral connected in the breaker box.
> There is also the possibility that they are connected elsewhere.
> These connections ate what will trip the gfi. Gfi just Checks for an
> unbalanced load between the hot and neutral.
> If the neutral and ground are connected some power may be transferred from
> the neutral to the ground and trip the gfi.
> Your gfi may be bad now because of this. Change to a new gfi and use your
> rv with a none gfi outlet should fix your short term problem.
> --
> 1977 Kingsley 455 as stock as it gets except lots of Ragusa parts
>
>

Miswires Yes

Dangerous Well not that much. Should be fixed to meet the code but no real danger. Don't forget that the NEC if set by committee and not all science.

I did look up the electric code from 1974 just to see if the ground and neutral should be separate at that point of time. And YES they should have even then.
non electricians over time do muck things up.
_______________________________________________
GMCnet mailing list
Unsubscribe or Change List Options:
http://list.gmcnet.org/mailman/listinfo/gmclist_list.gmcnet.org




1977 Kingsley 455 as stock as it gets except lots of Ragusa parts
Re: [GMCnet] plug into GFI outlet [message #332254 is a reply to message #332253] Thu, 17 May 2018 18:38 Go to previous messageGo to next message
James Hupy is currently offline  James Hupy   United States
Messages: 6806
Registered: May 2010
Karma: -62
Senior Member
If you make yourself into a better ground path than the conductors
themselves provide, you can be assured that electricity will find a way to
ground through you. If you do not consider that to be dangerous, I ponder
why you do not? I would not do that.
Jim Hupy

On Thu, May 17, 2018, 4:26 PM Mike Hamm wrote:

> Ken Henderson wrote on Thu, 17 May 2018 09:07
>> Mike, et al,
>>
>> Any GMC which has the ground and neutral connected in its breaker box is
>> MISWIRED and DANGEROUS. That connection should be made ONLY in the shore
>> power box. To understand this requirement, read this:
>>
>>
> https://docs.google.com/viewer?url=http%3A%2F%2Fwww.gmceast.com%2Ftechnical%2FBurton_Grounding_GMC_Motorhome.pdf
>> or
>> https://goo.gl/MW1lcP
>>
>> Ken H.
>>
>> On Thu, May 17, 2018 at 8:46 AM Mike Hamm wrote:
>>
>>> Most gmc's have the ground and neutral connected in the breaker box.
>>> There is also the possibility that they are connected elsewhere.
>>> These connections ate what will trip the gfi. Gfi just Checks for an
>>> unbalanced load between the hot and neutral.
>>> If the neutral and ground are connected some power may be transferred
> from
>>> the neutral to the ground and trip the gfi.
>>> Your gfi may be bad now because of this. Change to a new gfi and use
> your
>>> rv with a none gfi outlet should fix your short term problem.
>>> --
>>> 1977 Kingsley 455 as stock as it gets except lots of Ragusa parts
>>>
>>>
>>
>> Miswires Yes
>>
>> Dangerous Well not that much. Should be fixed to meet the code but no
> real danger. Don't forget that the NEC if set by committee and not all
>> science.
>>
>> I did look up the electric code from 1974 just to see if the ground and
> neutral should be separate at that point of time. And YES they should have
>> even then.
>> non electricians over time do muck things up.
>> _______________________________________________
>> GMCnet mailing list
>> Unsubscribe or Change List Options:
>> http://list.gmcnet.org/mailman/listinfo/gmclist_list.gmcnet.org
>
>
> --
> 1977 Kingsley 455 as stock as it gets except lots of Ragusa parts
>
> _______________________________________________
> GMCnet mailing list
> Unsubscribe or Change List Options:
> http://list.gmcnet.org/mailman/listinfo/gmclist_list.gmcnet.org
>
_______________________________________________
GMCnet mailing list
Unsubscribe or Change List Options:
http://list.gmcnet.org/mailman/listinfo/gmclist_list.gmcnet.org

Re: plug into GFI outlet [message #332257 is a reply to message #332173] Thu, 17 May 2018 20:34 Go to previous messageGo to next message
Ken Burton is currently offline  Ken Burton   United States
Messages: 10030
Registered: January 2004
Location: Hebron, Indiana
Karma: 10
Senior Member
I think I convinced Dick to change his instructions and he did it. You are correct. Connect distributor ground to something on the engine. The intake manifold it fine.

Ken Burton - N9KB
76 Palm Beach
Hebron, Indiana
Re: [GMCnet] plug into GFI outlet [message #332259 is a reply to message #332254] Thu, 17 May 2018 20:41 Go to previous messageGo to next message
Ken Henderson is currently offline  Ken Henderson   United States
Messages: 8726
Registered: March 2004
Location: Americus, GA
Karma: 9
Senior Member
You don't even have to be "better", just good enough to conduct 100 mA (0.1
A) or so at 170 volts (peak voltage 120 vac). That 1700 Ohms isn't hard to
achieve under wet conditions.

Ken H.


On Thu, May 17, 2018 at 7:39 PM James Hupy wrote:

> If you make yourself into a better ground path than the conductors
> themselves provide, you can be assured that electricity will find a way to
> ground through you. If you do not consider that to be dangerous, I ponder
> why you do not? I would not do that.
> Jim Hupy
>
> On Thu, May 17, 2018, 4:26 PM Mike Hamm wrote:
>
>> Ken Henderson wrote on Thu, 17 May 2018 09:07
>>> Mike, et al,
>>>
>>> Any GMC which has the ground and neutral connected in its breaker box
> is
>>> MISWIRED and DANGEROUS. That connection should be made ONLY in the
> shore
>>> power box. To understand this requirement, read this:
>>>
>>>
>>
> https://docs.google.com/viewer?url=http%3A%2F%2Fwww.gmceast.com%2Ftechnical%2FBurton_Grounding_GMC_Motorhome.pdf
>>> or
>>> https://goo.gl/MW1lcP
>>>
>>> Ken H.
>>>
>>> On Thu, May 17, 2018 at 8:46 AM Mike Hamm wrote:
>>>
>>>> Most gmc's have the ground and neutral connected in the breaker box.
>>>> There is also the possibility that they are connected elsewhere.
>>>> These connections ate what will trip the gfi. Gfi just Checks for an
>>>> unbalanced load between the hot and neutral.
>>>> If the neutral and ground are connected some power may be
> transferred
>> from
>>>> the neutral to the ground and trip the gfi.
>>>> Your gfi may be bad now because of this. Change to a new gfi and use
>> your
>>>> rv with a none gfi outlet should fix your short term problem.
>>>> --
>>>> 1977 Kingsley 455 as stock as it gets except lots of Ragusa parts
>>>>
>>>>
>>>
>>> Miswires Yes
>>>
>>> Dangerous Well not that much. Should be fixed to meet the code but no
>> real danger. Don't forget that the NEC if set by committee and not all
>>> science.
>>>
>>> I did look up the electric code from 1974 just to see if the ground and
>> neutral should be separate at that point of time. And YES they should
> have
>>> even then.
>>> non electricians over time do muck things up.
>>> _______________________________________________
>>> GMCnet mailing list
>>> Unsubscribe or Change List Options:
>>> http://list.gmcnet.org/mailman/listinfo/gmclist_list.gmcnet.org
>>
>>
>> --
>> 1977 Kingsley 455 as stock as it gets except lots of Ragusa parts
>>
>> _______________________________________________
>> GMCnet mailing list
>> Unsubscribe or Change List Options:
>> http://list.gmcnet.org/mailman/listinfo/gmclist_list.gmcnet.org
>>
> _______________________________________________
> GMCnet mailing list
> Unsubscribe or Change List Options:
> http://list.gmcnet.org/mailman/listinfo/gmclist_list.gmcnet.org
>
_______________________________________________
GMCnet mailing list
Unsubscribe or Change List Options:
http://list.gmcnet.org/mailman/listinfo/gmclist_list.gmcnet.org



Ken Henderson
Americus, GA
www.gmcwipersetc.com
Large Wiring Diagrams
76 X-Birchaven
76 X-Palm Beach
Re: plug into GFI outlet [message #332286 is a reply to message #332220] Fri, 18 May 2018 21:30 Go to previous messageGo to next message
Rick Staples is currently offline  Rick Staples   United States
Messages: 126
Registered: May 2014
Location: Johnstown, Colorado, USA
Karma: -1
Senior Member
[quote title=mghamms wrote on Thu, 17 May 2018 06:45]Most gmc's have the ground and neutral connected in the breaker box.
There is also the possibility that they are connected elsewhere.

This differed from my recollection from when I added new circuits and breakers for second AC and electric wall heater, etc to my early '75 Eleganza. So I went and checked the GM wiring diagrams, and no, the neutral and ground busses are NOT interconnected, at least on GM-finished coaches. If they ARE connected, it was probably the IPO at work. Be safe out there.

Rick Staples


Rick Staples, '75 Eleganza, Johnstown, CO "Advice is a dangerous gift, even from the Wise to the Wise, and all paths may run ill." -Tolkien
Re: plug into GFI outlet [message #332290 is a reply to message #332286] Sat, 19 May 2018 06:22 Go to previous messageGo to next message
kstockwell is currently offline  kstockwell   United States
Messages: 367
Registered: May 2016
Location: Putney VT
Karma: 4
Senior Member
Hi All,

I'm not dead, electrocuted, laying next to the coach, beer one hand.

I got to camp, and plugged into a GFI outside outlet (same as I did a month ago) and the outlet is not buzzing or tripping. So, I'm suspicious of the one at home.

Is there a way to test my plug? Can I plug into something (like a Kill-A-Watt type device that tells you about electrical usage) that could give me info on the electrical flow?

Thank you all for the responses. I was a little worried something had happened in the coach in the last month, but I am hopeful something happened at home.

Having the electrical info is really helpful. I'm on the cusp of getting one lithium battery to replace my golf carts and I wanted to take a good look at my electrical compartment; and where things go/what they do. I need to get the special lithium charging dongle for the IOTA, and I wanted to put the battery in the electrical box area; leaving the back where the 6v batteries are empty for my brand new macerator hose.)

kelly


1978 Kingsley Putney VT
Re: [GMCnet] plug into GFI outlet [message #332291 is a reply to message #332290] Sat, 19 May 2018 09:13 Go to previous messageGo to next message
Dave Stragand is currently offline  Dave Stragand   United States
Messages: 307
Registered: October 2017
Karma: 0
Senior Member
They have little outlet testers at the big box stores for around $5. Very easy to use.

https://www.homedepot.com/p/Power-Gear-3-Wire-Receptacle-Tester-50542/206212329

> On May 19, 2018, at 7:22 AM, kelly stockwell wrote:
>
> Hi All,
>
> I'm not dead, electrocuted, laying next to the coach, beer one hand.
>
> I got to camp, and plugged into a GFI outside outlet (same as I did a month ago) and the outlet is not buzzing or tripping. So, I'm suspicious of the
> one at home.
>
> Is there a way to test my plug? Can I plug into something (like a Kill-A-Watt type device that tells you about electrical usage) that could give me
> info on the electrical flow?
>
> Thank you all for the responses. I was a little worried something had happened in the coach in the last month, but I am hopeful something happened at
> home.
>
> Having the electrical info is really helpful. I'm on the cusp of getting one lithium battery to replace my golf carts and I wanted to take a good
> look at my electrical compartment; and where things go/what they do. I need to get the special lithium charging dongle for the IOTA, and I wanted to
> put the battery in the electrical box area; leaving the back where the 6v batteries are empty for my brand new macerator hose.)
>
> kelly
> --
> 1978 Kingsley
> Putney VT
>
> _______________________________________________
> GMCnet mailing list
> Unsubscribe or Change List Options:
> http://list.gmcnet.org/mailman/listinfo/gmclist_list.gmcnet.org
_______________________________________________
GMCnet mailing list
Unsubscribe or Change List Options:
http://list.gmcnet.org/mailman/listinfo/gmclist_list.gmcnet.org



1978 Transmode (403) Pittsburgh, PA
Re: plug into GFI outlet [message #332294 is a reply to message #332173] Sat, 19 May 2018 09:44 Go to previous messageGo to next message
JohnL455 is currently offline  JohnL455   United States
Messages: 4447
Registered: October 2006
Location: Woodstock, IL
Karma: 12
Senior Member
First, if the ground conductor in your power cable is intact, you should not get a shock even with a leakage to ground in the coach and no GFCI. Metal fatigue from improper coiling (kinking and twisting) can break the conductors in the cable set. Look for any areas with kinks, bulges or knots. You can buy a molded extension cord and cut off the female end and have the cord wired into your coach panel to keep factory molded construction. Since it works at camp you may be ok
Secondly you need to understand how GFCIs work. The current on the hot and neutral needs to be equal and opposite. Does not matter if you are using a little or a lot it needs to be the same "coming and going". If not then this tells the GFCI it is going somewhere it should not and instantly trip. If there is a bond between the N and G in the coach that will cause and instant trip as there are now 2 return paths and an imbalance between H and N. Sounds like your GFCI at home has a loose connection or the device has deteriorated. They do not do well in wet or humid Locations. Best to have it replaced and checked afterwards


John Lebetski
Woodstock, IL
77 Eleganza II
Re: plug into GFI outlet [message #332296 is a reply to message #332173] Sat, 19 May 2018 09:53 Go to previous messageGo to next message
JohnL455 is currently offline  JohnL455   United States
Messages: 4447
Registered: October 2006
Location: Woodstock, IL
Karma: 12
Senior Member
A tip is to always coil your power cable into the compartment using what we call in the entertainment industry as "over under" or "reverse coil". If you gently straighten out the cord and let all the twists come out, then reverse coil it into the compartment you will have zero twists when you extend it. Otherwise if you go round and round you will have one kink for every turn. This can cause the internal conductors to shift ruining the cable.

John Lebetski
Woodstock, IL
77 Eleganza II
Re: [GMCnet] plug into GFI outlet [message #332302 is a reply to message #332296] Sat, 19 May 2018 11:25 Go to previous messageGo to next message
James Hupy is currently offline  James Hupy   United States
Messages: 6806
Registered: May 2010
Karma: -62
Senior Member
I used to try to coil both hoses and long extension cords and almost always
fought with them. someone showed me how to handle them. Lay them out in a
straight line, and pull one end to the other. Drop them on the ground, walk
back to the middle, and pick it up, walk to the ends. Repeat, until you can
pick up the whole thing. To deploy, just take it out and give it a toss. It
will lay out, no kinks. If you coil it, it will tangle.
Jim Hupy

On Sat, May 19, 2018 at 7:53 AM, John R. Lebetski
wrote:

> A tip is to always coil your power cable into the compartment using what
> we call in the entertainment industry as "over under" or "reverse coil". If
> you gently straighten out the cord and let all the twists come out, then
> reverse coil it into the compartment you will have zero twists when you
> extend it. Otherwise if you go round and round you will have one kink for
> every turn. This can cause the internal conductors to shift ruining the
> cable.
> --
> John Lebetski
> Woodstock, IL
> 77 Eleganza II
>
>
> _______________________________________________
> GMCnet mailing list
> Unsubscribe or Change List Options:
> http://list.gmcnet.org/mailman/listinfo/gmclist_list.gmcnet.org
>
_______________________________________________
GMCnet mailing list
Unsubscribe or Change List Options:
http://list.gmcnet.org/mailman/listinfo/gmclist_list.gmcnet.org

Re: [GMCnet] plug into GFI outlet [message #332304 is a reply to message #332302] Sat, 19 May 2018 11:39 Go to previous messageGo to next message
Emery Stora is currently offline  Emery Stora   United States
Messages: 959
Registered: January 2011
Karma: 4
Senior Member

>
> On Sat, May 19, 2018 at 7:53 AM, John R. Lebetski
> wrote:
>
>> A tip is to always coil your power cable into the compartment using what
>> we call in the entertainment industry as "over under" or "reverse coil". If
>> you gently straighten out the cord and let all the twists come out, then
>> reverse coil it into the compartment you will have zero twists when you
>> extend it. Otherwise if you go round and round you will have one kink for
>> every turn. This can cause the internal conductors to shift ruining the
>> cable.
>> --
>> John Lebetski
>> Woodstock, IL
>> 77 Eleganza II
>>

John
You are too late warning me. I have been coiling my 50 (40) amp cable round and round for the 37 years that I have owned it.
When can I expect to have the cable ruined? :)

Emery Stora
77 Kingsley
Frederick, CO
_______________________________________________
GMCnet mailing list
Unsubscribe or Change List Options:
http://list.gmcnet.org/mailman/listinfo/gmclist_list.gmcnet.org

Re: [GMCnet] plug into GFI outlet [message #332305 is a reply to message #332304] Sat, 19 May 2018 11:57 Go to previous messageGo to previous message
Ken Henderson is currently offline  Ken Henderson   United States
Messages: 8726
Registered: March 2004
Location: Americus, GA
Karma: 9
Senior Member
Emery,

We need to have him give us lessons at the next rally -- I haven't been
able to figure it out for the past 81 years! Maybe we can get Kim to
schedule a seminar? :-)

Ken H.

On Sat, May 19, 2018 at 12:40 PM Emery Stora wrote:

>
>>
>> On Sat, May 19, 2018 at 7:53 AM, John R. Lebetski gransport7087@gmail.com>
>> wrote:
>>
>>> A tip is to always coil your power cable into the compartment using what
>>> we call in the entertainment industry as "over under" or "reverse
> coil". If
>>> you gently straighten out the cord and let all the twists come out, then
>>> reverse coil it into the compartment you will have zero twists when you
>>> extend it. Otherwise if you go round and round you will have one kink
> for
>>> every turn. This can cause the internal conductors to shift ruining the
>>> cable.
>>> --
>>> John Lebetski
>>> Woodstock, IL
>>> 77 Eleganza II
>>>
>
> John
> You are too late warning me. I have been coiling my 50 (40) amp cable
> round and round for the 37 years that I have owned it.
> When can I expect to have the cable ruined? :)
>
> Emery Stora
> 77 Kingsley
> Frederick, CO
> _______________________________________________
> GMCnet mailing list
> Unsubscribe or Change List Options:
> http://list.gmcnet.org/mailman/listinfo/gmclist_list.gmcnet.org
>
_______________________________________________
GMCnet mailing list
Unsubscribe or Change List Options:
http://list.gmcnet.org/mailman/listinfo/gmclist_list.gmcnet.org



Ken Henderson
Americus, GA
www.gmcwipersetc.com
Large Wiring Diagrams
76 X-Birchaven
76 X-Palm Beach
Previous Topic: Found a website with lots of brake design calculations
Next Topic: Re: [GMCnet] plug into GFI outlet (sort of)
Goto Forum:
  


Current Time: Sat Nov 16 20:02:09 CST 2024

Total time taken to generate the page: 0.01307 seconds