[GMCnet] 30 amp plug? [message #173529] Sat, 16 June 2012 13:33 Go to next message
KB is currently offline  KB   United States
Messages: 1262
Registered: September 2009
Karma: 0
Senior Member
I'm considering replacing the original 50 amp plug on the
coach with a 30 amp one. I've yet to see a 50 amp plug-in
at a campground, but frequently see the smaller ones.
We always end up with the unwieldy adapter plugs on the
end of the huge 50 amp oem plug, and effectively end up
with a single 15 or 20 amp 110 circuit.

The original wiring is four wires -- two hots, a neutral,
and a ground. The hot wires each power one-half of the main
breaker panel. In effect, two separate ~20 amp 110 circuits,
assuming you're plugged into a 50 amp outlet.

The 30 amp "camper" plugs I found are basically an oversize
110 plug with a single hot, neutral, and ground.

I can figure out the wiring from the plug to the main
box, but I haven't seen what to do with the Onan output.
Just ignore one hot wire? Rewire the Onan somehow??


thanks,
Karen
1973 23'
1975 26'


_______________________________________________
GMCnet mailing list
Unsubscribe or Change List Options:
http://temp.gmcnet.org/cgi-bin/mailman/listinfo/gmclist



Karen 1975 26' San Jose, CA
Re: [GMCnet] 30 amp plug? [message #173531 is a reply to message #173529] Sat, 16 June 2012 13:42 Go to previous messageGo to next message
Ken Henderson is currently offline  Ken Henderson   United States
Messages: 8726
Registered: March 2004
Location: Americus, GA
Karma: 9
Senior Member
Karen,

The Onan's already wired as you want it -- 120 vac to both legs of the 50A
cord (it's only wired for 120 vac). If you want to continue to transfer
from shore to Onan by moving the cord, just replace the Onan's 50A socket
with a 30A one.

I can certainly understand your desire to get rid of the 50A cable -- I
don't think I'd last a week with one of those; all Coachmen-fitted GMCs,
like my X-Birchaven came with 30A cords.

If you have two A/C's, and perhaps in other situations, you're likely to
find the 30A supply is not sufficient. What I did on my '90 Airstread Land
Yacht with 30A supply was add a separate 15A cord just for the rear A/C.
Most campsites seem to have both 30A and 15A outlets. For those with 50A
outlets, I carried a homemade adapter to split 50A to 30A & 15A sockets.

Ken H.


On Sat, Jun 16, 2012 at 2:33 PM, KB wrote:

> I'm considering replacing the original 50 amp plug on the
> coach with a 30 amp one. I've yet to see a 50 amp plug-in
> at a campground, but frequently see the smaller ones.
> We always end up with the unwieldy adapter plugs on the
> end of the huge 50 amp oem plug, and effectively end up
> with a single 15 or 20 amp 110 circuit.
>
> The original wiring is four wires -- two hots, a neutral,
> and a ground. The hot wires each power one-half of the main
> breaker panel. In effect, two separate ~20 amp 110 circuits,
> assuming you're plugged into a 50 amp outlet.
>
> The 30 amp "camper" plugs I found are basically an oversize
> 110 plug with a single hot, neutral, and ground.
>
> I can figure out the wiring from the plug to the main
> box, but I haven't seen what to do with the Onan output.
> Just ignore one hot wire? Rewire the Onan somehow??
>
>
_______________________________________________
GMCnet mailing list
Unsubscribe or Change List Options:
http://temp.gmcnet.org/cgi-bin/mailman/listinfo/gmclist



Ken Henderson
Americus, GA
www.gmcwipersetc.com
Large Wiring Diagrams
76 X-Birchaven
76 X-Palm Beach
Re: [GMCnet] 30 amp plug? [message #173535 is a reply to message #173531] Sat, 16 June 2012 14:15 Go to previous messageGo to next message
ljdavick is currently offline  ljdavick   United States
Messages: 3548
Registered: March 2007
Location: Fremont, CA
Karma: -3
Senior Member
My beloved PO installed a 30 amp cable, so I’ve never known the hassle of the 50 amp cable. I’ve never had trouble, though we only have one roof AC.

Larry Davick
The Mystery Machine
1976(ish) Palm Beach
Fremont, CA

On Jun 16, 2012, at 11:42 AM, Ken Henderson wrote:

> Karen,
>
> The Onan's already wired as you want it -- 120 vac to both legs of the 50A
> cord (it's only wired for 120 vac). If you want to continue to transfer
> from shore to Onan by moving the cord, just replace the Onan's 50A socket
> with a 30A one.
>
> I can certainly understand your desire to get rid of the 50A cable -- I
> don't think I'd last a week with one of those; all Coachmen-fitted GMCs,
> like my X-Birchaven came with 30A cords.
>
> If you have two A/C's, and perhaps in other situations, you're likely to
> find the 30A supply is not sufficient. What I did on my '90 Airstread Land
> Yacht with 30A supply was add a separate 15A cord just for the rear A/C.
> Most campsites seem to have both 30A and 15A outlets. For those with 50A
> outlets, I carried a homemade adapter to split 50A to 30A & 15A sockets.
>
> Ken H.
>

_______________________________________________
GMCnet mailing list
Unsubscribe or Change List Options:
http://temp.gmcnet.org/cgi-bin/mailman/listinfo/gmclist



Larry Davick
A Mystery Machine
1976(ish) Palm Beach
Fremont, Ca
Howell EFI + EBL + Electronic Dizzy
Re: [GMCnet] 30 amp plug? [message #173536 is a reply to message #173535] Sat, 16 June 2012 14:33 Go to previous messageGo to next message
k2gkk is currently offline  k2gkk   United States
Messages: 4452
Registered: November 2009
Karma: -8
Senior Member

Money Pit (Pig) has the 50A plug/cable combo.
I would not even begin to think about removing
50A service to get a smaller cable. I don't
want to take the chance that my 2 A/C units
would be supported from a 30A source and two
are needed here in Oklahoma. We needed both at
Shawnee in March!

What I am going to do, is to cut the standard
shore power cable that fits into the Onan's
output receptacle down to a manageable length.
The male end of that cable needs replacement anyway
as it has suffered mangling and the ground pin is
intermittent. I will make an extension cable from
the remainder with female and male ends. The two
will store far more easily under one of the dinette
benches and along with the OTHER 30' extension I
have will allow options for various lengths of
power hookup.

~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~
~~ ~ D C "Mac" Macdonald ~ ~~
~ ~ Amateur Radio - K2GKK ~ ~
~ ~ USAF and FAA, Retired ~ ~
~ ~ ~ Oklahoma City, OK ~ ~ ~
~~ ~ ~ "The Money Pit" ~ ~ ~~
~ ~ ~ '76 ex-Palm Beach ~ ~ ~
~ www.gmcmhphotos.com/okclb ~
~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~
______________
*[ ]~~~[][ ][|\
*--OO--[]---O-*





> From: ljdavick@comcast.net
> Date: Sat, 16 Jun 2012 12:15:50 -0700
> To: gmclist@temp.gmcnet.org
> Subject: Re: [GMCnet] 30 amp plug?
>
> My beloved PO installed a 30 amp cable, so I’ve never known the hassle of the 50 amp cable. I’ve never had trouble, though we only have one roof AC.
>
> Larry Davick
> The Mystery Machine
> 1976(ish) Palm Beach
> Fremont, CA
>
> On Jun 16, 2012, at 11:42 AM, Ken Henderson wrote:
>
> > Karen,
> >
> > The Onan's already wired as you want it -- 120 vac to both legs of the 50A
> > cord (it's only wired for 120 vac). If you want to continue to transfer
> > from shore to Onan by moving the cord, just replace the Onan's 50A socket
> > with a 30A one.
> >
> > I can certainly understand your desire to get rid of the 50A cable -- I
> > don't think I'd last a week with one of those; all Coachmen-fitted GMCs,
> > like my X-Birchaven came with 30A cords.
> >
> > If you have two A/C's, and perhaps in other situations, you're likely to
> > find the 30A supply is not sufficient. What I did on my '90 Airstread Land
> > Yacht with 30A supply was add a separate 15A cord just for the rear A/C.
> > Most campsites seem to have both 30A and 15A outlets. For those with 50A
> > outlets, I carried a homemade adapter to split 50A to 30A & 15A sockets.
> >
> > Ken H.

_______________________________________________
GMCnet mailing list
Unsubscribe or Change List Options:
http://temp.gmcnet.org/cgi-bin/mailman/listinfo/gmclist

Re: [GMCnet] 30 amp plug? [message #173537 is a reply to message #173529] Sat, 16 June 2012 14:38 Go to previous messageGo to next message
RF_Burns is currently offline  RF_Burns   Canada
Messages: 2277
Registered: June 2008
Location: S. Ontario, Canada
Karma: 3
Senior Member
I found a short 50 plug & 6' cord and wired that to the fuse panel. Then I put a 50 Amp female socket on the end of the original cord and stored it in the pod in case I ever needed it, (I left it at home after a few months).

Now I can plug into the 50Amp Onan socket, or use an adaptor and a 30Amp extension.

I don't miss having to roll up that heavy 50Amp cord and jam it into the storage box.

Be sure to get a full 50Amp cord. An oven/dryer style cord is designed for 220V where the neutral carries very little current and sometimes is a smaller gauge. In our application the neutral carries the full current and needs to be larger.


Bruce Hislop
ON Canada
77PB, 455 Dick P. rebuilt, DynamicEFI EBL EFI & ESC.
1 ton front end
http://www.gmcmhphotos.com/photos/showphoto.php?photo=29001
My Staff says I never listen to them, or something like that
Re: [GMCnet] 30 amp plug? [message #173538 is a reply to message #173529] Sat, 16 June 2012 14:57 Go to previous messageGo to next message
rssbob is currently offline  rssbob   United States
Messages: 259
Registered: January 2004
Location: La Mesa, Ca. (San Diego a...
Karma: 0
Senior Member

On Jun 16, 2012, at 11:33 AM, KB wrote:

> I'm considering replacing the original 50 amp plug on the
> coach with a 30 amp one. I've yet to see a 50 amp plug-in
> at a campground, but frequently see the smaller ones.
> We always end up with the unwieldy adapter plugs on the
> end of the huge 50 amp oem plug, and effectively end up
> with a single 15 or 20 amp 110 circuit.
>
> The original wiring is four wires -- two hots, a neutral,
> and a ground. The hot wires each power one-half of the main
> breaker panel. In effect, two separate ~20 amp 110 circuits,
> assuming you're plugged into a 50 amp outlet.
>
> The 30 amp "camper" plugs I found are basically an oversize
> 110 plug with a single hot, neutral, and ground.
>
> I can figure out the wiring from the plug to the main
> box, but I haven't seen what to do with the Onan output.
> Just ignore one hot wire? Rewire the Onan somehow??
>
>
> thanks,
> Karen
> 1973 23'
> 1975 26'
>
>
> _______________________________________________
> GMCnet mailing list
> Unsubscribe or Change List Options:
> http://temp.gmcnet.org/cgi-bin/mailman/listinfo/gmclist
Hi Karen,

Here is what I did with my 50 amp power cable.

1. Cut the cord off so you will have enough cable left to reinstall the plug on the stub. It needs to be long enough to plug into the gen set. I left mine about 4' long and if I had it to do over I would have left it about 2 feet long.

2. With the old 50 amp cable you have left you can put another connector on the cutt-off en to make it into a 50 amp extension cord. Then if you ever need 50 amps you can use this instead of the 30 amp.

http://www.gmcmhphotos.com/photos/g3777-power-cord-update.html


Bob Sobrito
1978 Palm Beach
La Mesa, Ca
antique pocket watch repair

_______________________________________________
GMCnet mailing list
Unsubscribe or Change List Options:
http://temp.gmcnet.org/cgi-bin/mailman/listinfo/gmclist



Bob Sobrito
78 Palm Beach
La Mesa, Ca
Re: [GMCnet] 30 amp plug? [message #173539 is a reply to message #173537] Sat, 16 June 2012 14:59 Go to previous messageGo to next message
emerystora is currently offline  emerystora   United States
Messages: 4442
Registered: January 2004
Karma: 13
Senior Member

On Jun 16, 2012, at 1:38 PM, Bruce Hislop <bruce@perthcomm.com> wrote:

>
>
> I found a short 50 plug & 6' cord and wired that to the fuse panel. Then I put a 50 Amp female socket on the end of the original cord and stored it in the pod in case I ever needed it, (I left it at home after a few months).
>
> Now I can plug into the 50Amp Onan socket, or use an adaptor and a 30Amp extension.
>
> I don't miss having to roll up that heavy 50Amp cord and jam it into the storage box.
>
>
Just as a point of information, GM did not use a 50 amp cable. They used a 40 amp cable. If you look at the printing on an original cable you would see that it reads "40 amps". This matches the two 20 amp breakers inside the motorhome.

The plug and receptacle are the same as 50 amp equipment which is why many people assume that the cable also is.

Emery Stora
_______________________________________________
GMCnet mailing list
Unsubscribe or Change List Options:
http://temp.gmcnet.org/cgi-bin/mailman/listinfo/gmclist

Re: [GMCnet] 30 amp plug? [message #173540 is a reply to message #173535] Sat, 16 June 2012 14:54 Go to previous messageGo to next message
emerystora is currently offline  emerystora   United States
Messages: 4442
Registered: January 2004
Karma: 13
Senior Member
Funny, but I've never found the 50 amp cable (actually 40 amp) to be a hassle. I will never change it.

You may need me or someone else to show you the proper way to roll the cable into the compartment. Even in below zero weather I've never had a problem doing it.

Plus it's great to have full 40 amp service.

Emery Stora

On Jun 16, 2012, at 1:15 PM, Larry Davick <ljdavick@comcast.net> wrote:

> My beloved PO installed a 30 amp cable, so I’ve never known the hassle of the 50 amp cable. I’ve never had trouble, though we only have one roof AC.
>
> Larry Davick
> The Mystery Machine
> 1976(ish) Palm Beach
> Fremont, CA
>
> On Jun 16, 2012, at 11:42 AM, Ken Henderson wrote:
>
>> Karen,
>>
>> The Onan's already wired as you want it -- 120 vac to both legs of the 50A
>> cord (it's only wired for 120 vac). If you want to continue to transfer
>> from shore to Onan by moving the cord, just replace the Onan's 50A socket
>> with a 30A one.
>>
>> I can certainly understand your desire to get rid of the 50A cable -- I
>> don't think I'd last a week with one of those; all Coachmen-fitted GMCs,
>> like my X-Birchaven came with 30A cords.
>>
>> If you have two A/C's, and perhaps in other situations, you're likely to
>> find the 30A supply is not sufficient. What I did on my '90 Airstread Land
>> Yacht with 30A supply was add a separate 15A cord just for the rear A/C.
>> Most campsites seem to have both 30A and 15A outlets. For those with 50A
>> outlets, I carried a homemade adapter to split 50A to 30A & 15A sockets.
>>
>> Ken H.
>>
>
> _______________________________________________
> GMCnet mailing list
> Unsubscribe or Change List Options:
> http://temp.gmcnet.org/cgi-bin/mailman/listinfo/gmclist
_______________________________________________
GMCnet mailing list
Unsubscribe or Change List Options:
http://temp.gmcnet.org/cgi-bin/mailman/listinfo/gmclist
Re: [GMCnet] 30 amp plug? [message #173541 is a reply to message #173540] Sat, 16 June 2012 15:16 Go to previous messageGo to next message
k2gkk is currently offline  k2gkk   United States
Messages: 4452
Registered: November 2009
Karma: -8
Senior Member

My mother's second husband, a sailboater, taught me the trick
of which you are probably speaking. It's still a bit of a hassle,
but the cable WILL fit!

~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~
~~ ~ D C "Mac" Macdonald ~ ~~
~ ~ Amateur Radio - K2GKK ~ ~
~ ~ USAF and FAA, Retired ~ ~
~ ~ ~ Oklahoma City, OK ~ ~ ~
~~ ~ ~ "The Money Pit" ~ ~ ~~
~ ~ ~ '76 ex-Palm Beach ~ ~ ~
~ www.gmcmhphotos.com/okclb ~
~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~
______________
*[ ]~~~[][ ][|\
*--OO--[]---O-*




> From: emerystora@mac.com
> Date: Sat, 16 Jun 2012 13:54:57 -0600
> To: gmclist@temp.gmcnet.org
> Subject: Re: [GMCnet] 30 amp plug?
>
> Funny, but I've never found the 50 amp cable (actually 40 amp) to be a hassle. I will never change it.
>
> You may need me or someone else to show you the proper way to roll the cable into the compartment. Even in below zero weather I've never had a problem doing it.
>
> Plus it's great to have full 40 amp service.
>
> Emery Stora

_______________________________________________
GMCnet mailing list
Unsubscribe or Change List Options:
http://temp.gmcnet.org/cgi-bin/mailman/listinfo/gmclist

Re: [GMCnet] 30 amp plug? [message #173547 is a reply to message #173541] Sat, 16 June 2012 16:40 Go to previous messageGo to next message
Chuck Garton is currently offline  Chuck Garton   United States
Messages: 54
Registered: June 2006
Karma: 0
Member
I had a 1974 coach for 16 years and its 50A cable was a pain, very
stiff even when warm. My 1977 coach' 50A cable is very flexable even
when its cold. I checked other newer coaches and their cables are like
mine.
Having 2 roof A/C's and living in the desert, I'll keep the 50A.

Chuck Garton
77 Kingsley 455
Ridgecrest, CA

On Sat, Jun 16, 2012 at 1:16 PM, D C *Mac* Macdonald <k2gkk@hotmail.com> wrote:
>
> My mother's second husband, a sailboater, taught me the trick
> of which you are probably speaking. It's still a bit of a hassle,
> but the cable WILL fit!
>
> ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~
> ~~ ~ D C "Mac" Macdonald ~ ~~
> ~ ~ Amateur Radio - K2GKK ~ ~
> ~ ~ USAF and FAA, Retired ~ ~
> ~ ~ ~ Oklahoma City, OK ~ ~ ~
> ~~ ~ ~ "The Money Pit" ~ ~ ~~
> ~ ~ ~ '76 ex-Palm Beach ~ ~ ~
> ~ www.gmcmhphotos.com/okclb ~
> ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~
> ______________
> *[ ]~~~[][ ][|\
> *--OO--[]---O-*
>
>
>
>
>> From: emerystora@mac.com
>> Date: Sat, 16 Jun 2012 13:54:57 -0600
>> To: gmclist@temp.gmcnet.org
>> Subject: Re: [GMCnet] 30 amp plug?
>>
>> Funny, but I've never found the 50 amp cable (actually 40 amp) to be a hassle. I will never change it.
>>
>> You may need me or someone else to show you the proper way to roll the cable into the compartment. Even in below zero weather I've never had a problem doing it.
>>
>> Plus it's great to have full 40 amp service.
>>
>> Emery Stora
>
> _______________________________________________
> GMCnet mailing list
> Unsubscribe or Change List Options:
> http://temp.gmcnet.org/cgi-bin/mailman/listinfo/gmclist
_______________________________________________
GMCnet mailing list
Unsubscribe or Change List Options:
http://temp.gmcnet.org/cgi-bin/mailman/listinfo/gmclist

Re: [GMCnet] 30 amp plug? [message #173548 is a reply to message #173547] Sat, 16 June 2012 16:43 Go to previous messageGo to next message
emerystora is currently offline  emerystora   United States
Messages: 4442
Registered: January 2004
Karma: 13
Senior Member
Chuck

It never occurred to me that eariler models may have had different, less flexible, cables from that in my 1977.

Perhaps that is why I've never had a problem with it.

Emery Stora

On Jun 16, 2012, at 3:40 PM, Chuck Garton <ceg777@earthlink.net> wrote:

> I had a 1974 coach for 16 years and its 50A cable was a pain, very
> stiff even when warm. My 1977 coach' 50A cable is very flexable even
> when its cold. I checked other newer coaches and their cables are like
> mine.
> Having 2 roof A/C's and living in the desert, I'll keep the 50A.
>
> Chuck Garton
> 77 Kingsley 455
> Ridgecrest, CA
>
> On Sat, Jun 16, 2012 at 1:16 PM, D C *Mac* Macdonald <k2gkk@hotmail.com> wrote:
>>
>> My mother's second husband, a sailboater, taught me the trick
>> of which you are probably speaking. It's still a bit of a hassle,
>> but the cable WILL fit!
>>
>> ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~
>> ~~ ~ D C "Mac" Macdonald ~ ~~
>> ~ ~ Amateur Radio - K2GKK ~ ~
>> ~ ~ USAF and FAA, Retired ~ ~
>> ~ ~ ~ Oklahoma City, OK ~ ~ ~
>> ~~ ~ ~ "The Money Pit" ~ ~ ~~
>> ~ ~ ~ '76 ex-Palm Beach ~ ~ ~
>> ~ www.gmcmhphotos.com/okclb ~
>> ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~
>> ______________
>> *[ ]~~~[][ ][|\
>> *--OO--[]---O-*
>>
>>
>>
>>
>>> From: emerystora@mac.com
>>> Date: Sat, 16 Jun 2012 13:54:57 -0600
>>> To: gmclist@temp.gmcnet.org
>>> Subject: Re: [GMCnet] 30 amp plug?
>>>
>>> Funny, but I've never found the 50 amp cable (actually 40 amp) to be a hassle. I will never change it.
>>>
>>> You may need me or someone else to show you the proper way to roll the cable into the compartment. Even in below zero weather I've never had a problem doing it.
>>>
>>> Plus it's great to have full 40 amp service.
>>>
>>> Emery Stora
>>
>> _______________________________________________
>> GMCnet mailing list
>> Unsubscribe or Change List Options:
>> http://temp.gmcnet.org/cgi-bin/mailman/listinfo/gmclist
> _______________________________________________
> GMCnet mailing list
> Unsubscribe or Change List Options:
> http://temp.gmcnet.org/cgi-bin/mailman/listinfo/gmclist
_______________________________________________
GMCnet mailing list
Unsubscribe or Change List Options:
http://temp.gmcnet.org/cgi-bin/mailman/listinfo/gmclist

Re: [GMCnet] 30 amp plug? [message #173549 is a reply to message #173548] Sat, 16 June 2012 16:55 Go to previous messageGo to next message
ljdavick is currently offline  ljdavick   United States
Messages: 3548
Registered: March 2007
Location: Fremont, CA
Karma: -3
Senior Member
It dawns on me that part of the problem is the plugging/unplugging of the cable to the Onan. My beloved PO installed an automatic shoreline switch so that I needn’t worry about such things.

The 30 amp cable works for me. YMMV.

Larry Davick
The Mystery Machine
1976(ish) Palm Beach
Fremont, CA

On Jun 16, 2012, at 2:43 PM, Emery Stora wrote:

> Chuck
>
> It never occurred to me that eariler models may have had different, less flexible, cables from that in my 1977.
>
> Perhaps that is why I've never had a problem with it.
>
> Emery Stora
>

_______________________________________________
GMCnet mailing list
Unsubscribe or Change List Options:
http://temp.gmcnet.org/cgi-bin/mailman/listinfo/gmclist



Larry Davick
A Mystery Machine
1976(ish) Palm Beach
Fremont, Ca
Howell EFI + EBL + Electronic Dizzy
Re: [GMCnet] 30 amp plug? [message #173550 is a reply to message #173548] Sat, 16 June 2012 17:16 Go to previous messageGo to next message
k2gkk is currently offline  k2gkk   United States
Messages: 4452
Registered: November 2009
Karma: -8
Senior Member

I suspect that 50A 125/250V capable cable is
pretty much "standard" and GMC MAY have used
it on earlier coaches instead of dropping to
40A capability to save a few dollars.

Mine is quite stiff, even in warm temperatures.
I had the final pair of KMC XD 775 Rock Star
wheels put on last week and the in and out
drill is somewhat difficult, even in warmer
weather.

~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~
~~ ~ D C "Mac" Macdonald ~ ~~
~ ~ Amateur Radio - K2GKK ~ ~
~ ~ USAF and FAA, Retired ~ ~
~ ~ ~ Oklahoma City, OK ~ ~ ~
~~ ~ ~ "The Money Pit" ~ ~ ~~
~ ~ ~ '76 ex-Palm Beach ~ ~ ~
~ www.gmcmhphotos.com/okclb ~
~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~
______________
*[ ]~~~[][ ][|\
*--OO--[]---O-*





> From: emerystora@mac.com
> Date: Sat, 16 Jun 2012 15:43:56 -0600
> To: gmclist@temp.gmcnet.org
> Subject: Re: [GMCnet] 30 amp plug?
>
> Chuck
>
> It never occurred to me that eariler models may have had different, less flexible, cables from that in my 1977.
>
> Perhaps that is why I've never had a problem with it.
>
> Emery Stora
>
> On Jun 16, 2012, at 3:40 PM, Chuck Garton <ceg777@earthlink.net> wrote:
>
> > I had a 1974 coach for 16 years and its 50A cable was a pain, very
> > stiff even when warm. My 1977 coach' 50A cable is very flexable even
> > when its cold. I checked other newer coaches and their cables are like
> > mine.
> > Having 2 roof A/C's and living in the desert, I'll keep the 50A.
> >
> > Chuck Garton
> > 77 Kingsley 455
> > Ridgecrest, CA
> >>
> >>
> >>> From: emerystora@mac.com
> >>> Date: Sat, 16 Jun 2012 13:54:57 -0600
> >>> To: gmclist@temp.gmcnet.org
> >>> Subject: Re: [GMCnet] 30 amp plug?
> >>>
> >>> Funny, but I've never found the 50 amp cable (actually 40 amp) to be a hassle. I will never change it.
> >>>
> >>> You may need me or someone else to show you the proper way to roll the cable into the compartment. Even in below zero weather I've never had a problem doing it.
> >>>
> >>> Plus it's great to have full 40 amp service.
> >>>
> >>> Emery Stora

_______________________________________________
GMCnet mailing list
Unsubscribe or Change List Options:
http://temp.gmcnet.org/cgi-bin/mailman/listinfo/gmclist

Re: [GMCnet] 30 amp plug? [message #173567 is a reply to message #173540] Sat, 16 June 2012 18:57 Go to previous messageGo to next message
USAussie is currently offline  USAussie   United States
Messages: 15912
Registered: July 2007
Location: Sydney, Australia
Karma: 6
Senior Member
Emery,

Avions have a 50 amp cable and while it is stiff when cold it's not that
difficult to coil it up in the galvanized storage box. I push on it while
shoving it in which keeps it up against the ID of the box and leaves enough
room in the center to store all the electrical adaptors and all the water
connection bits and pieces.

At one time I considered replacing it with a new cable that had thin multi
stranded wire but the cost of the cable killed that idea!

Regards,
Rob M.
 
-----Original Message-----
From: Emery Stora

Funny, but I've never found the 50 amp cable (actually 40 amp) to be a
hassle. I will never change it.

You may need me or someone else to show you the proper way to roll the cable
into the compartment. Even in below zero weather I've never had a problem
doing it.

Plus it's great to have full 40 amp service.

Emery Stora


_______________________________________________
GMCnet mailing list
Unsubscribe or Change List Options:
http://temp.gmcnet.org/cgi-bin/mailman/listinfo/gmclist



Regards, Rob M. (USAussie) The Pedantic Mechanic Sydney, Australia '75 Avion - AUS - The Blue Streak TZE365V100428 '75 Avion - USA - Double Trouble TZE365V100426
Re: [GMCnet] 30 amp plug? [message #173579 is a reply to message #173540] Sat, 16 June 2012 20:12 Go to previous messageGo to next message
bukzin is currently offline  bukzin   United States
Messages: 840
Registered: April 2004
Location: North California
Karma: 0
Senior Member
[quote title=emerystora wrote on Sat, 16 June 2012 12:54]Funny, but I've never found the 50 amp cable (actually 40 amp) to be a hassle. I will never change it.

You may need me or someone else to show you the proper way to roll the cable into the compartment. Even in below zero weather I've never had a problem doing it.

Plus it's great to have full 40 amp service.

Emery Stora


More power. More better.


Bukzin
1977 Palm Beach
Re: [GMCnet] 30 amp plug? [message #173581 is a reply to message #173529] Sat, 16 June 2012 20:18 Go to previous messageGo to next message
KB is currently offline  KB   United States
Messages: 1262
Registered: September 2009
Karma: 0
Senior Member
I don't mind the cord too much. The problem is we have
yet to visit a campground that actually had a 50amp outlet.
Regular 15 or 20 amp and the "camper" 30 amp outlets is
all we've seen. But maybe it's regional.

Sounds like the wiring solution is to just cap off one of the
hots from the onan and only use one leg for the 30amp outlet.


thanks
Karen
1973 23'
1975 26'



_______________________________________________
GMCnet mailing list
Unsubscribe or Change List Options:
http://temp.gmcnet.org/cgi-bin/mailman/listinfo/gmclist



Karen 1975 26' San Jose, CA
Re: [GMCnet] 30 amp plug? [message #173585 is a reply to message #173581] Sat, 16 June 2012 20:32 Go to previous messageGo to next message
USAussie is currently offline  USAussie   United States
Messages: 15912
Registered: July 2007
Location: Sydney, Australia
Karma: 6
Senior Member
Karen,

I agree not all campgrounds have 50 amp plugs which is why I carry:

1) female 50 amp to male 30 amp adapter
2) male 50 amp to 30 amp female
3) female 30 amp to 10 amp male
4) 25 foot 30 amp female 30 amp male extension cord
5) two 25 foot 10 amp female to 10 amp male extension cords

I think I have one more adapter but I can't remember what it is.

In case you're wondering EVERYTHING above and the H2O adapters all fit in
the galvanized box on the side of the Avion.

Regards,
Rob M.

-----Original Message-----
From: KB

I don't mind the cord too much. The problem is we have
yet to visit a campground that actually had a 50amp outlet.
Regular 15 or 20 amp and the "camper" 30 amp outlets is
all we've seen. But maybe it's regional.

Sounds like the wiring solution is to just cap off one of the
hots from the onan and only use one leg for the 30amp outlet.

thanks
Karen

_______________________________________________
GMCnet mailing list
Unsubscribe or Change List Options:
http://temp.gmcnet.org/cgi-bin/mailman/listinfo/gmclist



Regards, Rob M. (USAussie) The Pedantic Mechanic Sydney, Australia '75 Avion - AUS - The Blue Streak TZE365V100428 '75 Avion - USA - Double Trouble TZE365V100426
Re: [GMCnet] 30 amp plug? [message #173608 is a reply to message #173585] Sat, 16 June 2012 22:48 Go to previous messageGo to next message
Ken Burton is currently offline  Ken Burton   United States
Messages: 10030
Registered: January 2004
Location: Hebron, Indiana
Karma: 10
Senior Member
I pulled in to a campground for a one night overnight stop. I do not remember where it was now other than the WiFi was terrible, The lady said I only have one spot left. It is 50 amp only. I took it. I know of no commercially available adapter to go from a 30 amp 110 coach to a 50 amp 220 service. I realize I could make one and carry it with me if I had 30 amp service. Most places I have stayed at, including most GMCMI rallies, offer 50, 30, and 20 or 15 amp service.



Ken Burton - N9KB
76 Palm Beach
Hebron, Indiana
Re: [GMCnet] 30 amp plug? [message #173612 is a reply to message #173585] Sat, 16 June 2012 23:11 Go to previous messageGo to next message
emerystora is currently offline  emerystora   United States
Messages: 4442
Registered: January 2004
Karma: 13
Senior Member
I carry those but I also have a 50 amp fe mail to a 15 amp mail. This is hard to find but very handy as it prevents having to use two or three adapters in series.

Emery Stora

On Jun 16, 2012, at 7:32 PM, Robert Mueller <robmueller@iinet.net.au> wrote:

> Karen,
>
> I agree not all campgrounds have 50 amp plugs which is why I carry:
>
> 1) female 50 amp to male 30 amp adapter
> 2) male 50 amp to 30 amp female
> 3) female 30 amp to 10 amp male
> 4) 25 foot 30 amp female 30 amp male extension cord
> 5) two 25 foot 10 amp female to 10 amp male extension cords
>
> I think I have one more adapter but I can't remember what it is.
>
> In case you're wondering EVERYTHING above and the H2O adapters all fit in
> the galvanized box on the side of the Avion.
>
> Regards,
> Rob M.
>
> -----Original Message-----
> From: KB
>
> I don't mind the cord too much. The problem is we have
> yet to visit a campground that actually had a 50amp outlet.
> Regular 15 or 20 amp and the "camper" 30 amp outlets is
> all we've seen. But maybe it's regional.
>
> Sounds like the wiring solution is to just cap off one of the
> hots from the onan and only use one leg for the 30amp outlet.
>
> thanks
> Karen
>
> _______________________________________________
> GMCnet mailing list
> Unsubscribe or Change List Options:
> http://temp.gmcnet.org/cgi-bin/mailman/listinfo/gmclist
_______________________________________________
GMCnet mailing list
Unsubscribe or Change List Options:
http://temp.gmcnet.org/cgi-bin/mailman/listinfo/gmclist

Re: [GMCnet] 30 amp plug? [message #173644 is a reply to message #173529] Sun, 17 June 2012 11:26 Go to previous messageGo to previous message
KB is currently offline  KB   United States
Messages: 1262
Registered: September 2009
Karma: 0
Senior Member

Maybe best to get a 50 to 30amp adapter like this and be done with it:

http://www.adventurerv.net/amp-female-amp-male-adapter-p-122.html


thanks,
Karen
1973 23'
1975 26'
_______________________________________________
GMCnet mailing list
Unsubscribe or Change List Options:
http://temp.gmcnet.org/cgi-bin/mailman/listinfo/gmclist



Karen 1975 26' San Jose, CA
Previous Topic: [GMCnet] Paint stripe removal
Next Topic: Wifi/internet connections for travel
Goto Forum:
  


Current Time: Tue Feb 04 07:44:31 CST 2025

Total time taken to generate the page: 0.25327 seconds