Honda EV4010 problem [message #137764] Sat, 06 August 2011 14:10 Go to next message
bernie is currently offline  bernie   Canada
Messages: 46
Registered: February 2008
Location: Montreal
Karma: 0
Member
My Honda EV4010 generator runs fine except:

When a high amp load is required( like when the A/C compressor
kicks in ) the generator runs Ok BUT when the A/C compressor kicks out, the RPM goes wild (high and low, again and again) until the A/C compressor kicks in again...and the RPM returns to stable condition...


Bernard GMC Transmode 1977 Montreal,Canada
Re: [GMCnet] Honda EV4010 problem [message #137768 is a reply to message #137764] Sat, 06 August 2011 15:40 Go to previous messageGo to next message
James Hupy is currently offline  James Hupy   United States
Messages: 6806
Registered: May 2010
Karma: -62
Senior Member
Nothin' runs like a Honda! Sounds like the governor needs to be adjusted.
Jim Hupy
Salem, OR
78 GMC Royale 403

On Sat, Aug 6, 2011 at 12:10 PM, Bernard <danxavfan@gmail.com> wrote:

>
>
> My Honda EV4010 generator runs fine except:
>
> When a high amp load is required( like when the A/C compressor
> kicks in ) the generator runs Ok BUT when the A/C compressor kicks out, the
> RPM goes wild (high and low, again and again) until the A/C compressor kicks
> in again...and the RPM returns to stable condition...
> --
> Bernard
> GMC Transmode 1977
> Montreal,Canada
> _______________________________________________
> GMCnet mailing list
> Unsubscribe or Change List Options:
> http://temp.gmcnet.org/cgi-bin/mailman/listinfo/gmclist
>
_______________________________________________
GMCnet mailing list
Unsubscribe or Change List Options:
http://temp.gmcnet.org/cgi-bin/mailman/listinfo/gmclist

Re: [GMCnet] Honda EV4010 problem [message #137770 is a reply to message #137764] Sat, 06 August 2011 16:31 Go to previous messageGo to next message
jhbridges is currently offline  jhbridges   United States
Messages: 8412
Registered: May 2011
Location: Braselton ga
Karma: -74
Senior Member
Is that a variable speed (inverter)  generator?  See if there isn't   control on the PC board called 'loop gain' or something like.  Try turning it slightly in either direction and see if the condition doesn't get better in one direction.
 
--johnny

--- On Sat, 8/6/11, Bernard <danxavfan@gmail.com> wrote:


From: Bernard <danxavfan@gmail.com>
Subject: [GMCnet] Honda EV4010 problem
To: gmclist@temp.gmcnet.org
Date: Saturday, August 6, 2011, 7:10 PM




My Honda EV4010 generator runs fine except:

When  a high amp load is required( like when the A/C compressor
kicks in ) the generator runs Ok BUT when the A/C compressor kicks out, the RPM goes wild (high and low, again and again) until the A/C compressor kicks in again...and the RPM returns to stable condition...
--
Bernard
GMC Transmode 1977
Montreal,Canada
_______________________________________________
GMCnet mailing list
Unsubscribe or Change List Options:
http://temp.gmcnet.org/cgi-bin/mailman/listinfo/gmclist
_______________________________________________
GMCnet mailing list
Unsubscribe or Change List Options:
http://temp.gmcnet.org/cgi-bin/mailman/listinfo/gmclist



Foolish Carriage, 76 26' Eleganza(?) with beaucoup mods and add - ons. Braselton, Ga. I forgive them all, save those who hurt the dogs. They must answer to me in hell
Re: [GMCnet] Honda EV4010 problem [message #137771 is a reply to message #137768] Sat, 06 August 2011 16:39 Go to previous messageGo to next message
bernie is currently offline  bernie   Canada
Messages: 46
Registered: February 2008
Location: Montreal
Karma: 0
Member
That's what I thought(governor)...Do you know how to adjust it ? Where is the adjustment ?

Bernard GMC Transmode 1977 Montreal,Canada

[Updated on: Sat, 06 August 2011 16:40]

Report message to a moderator

Re: [GMCnet] Honda EV4010 problem [message #137773 is a reply to message #137771] Sat, 06 August 2011 16:45 Go to previous messageGo to next message
jhbridges is currently offline  jhbridges   United States
Messages: 8412
Registered: May 2011
Location: Braselton ga
Karma: -74
Senior Member
On that one, I dunno.  It may even be mechanical.  But a hypersensitive governor system will hunt like that.  My Junkerac is currently doing it, but I'm in Illinois at a show this weekend, can't fiddle with it till I get home.
 
--johnny

--- On Sat, 8/6/11, Bernard <danxavfan@gmail.com> wrote:


From: Bernard <danxavfan@gmail.com>
Subject: Re: [GMCnet] Honda EV4010 problem
To: gmclist@temp.gmcnet.org
Date: Saturday, August 6, 2011, 9:39 PM




That's what I thought...Do you know how to adjust it ? Where is the adjustment ?
--
Bernard
GMC Transmode 1977
Montreal,Canada
_______________________________________________
GMCnet mailing list
Unsubscribe or Change List Options:
http://temp.gmcnet.org/cgi-bin/mailman/listinfo/gmclist
_______________________________________________
GMCnet mailing list
Unsubscribe or Change List Options:
http://temp.gmcnet.org/cgi-bin/mailman/listinfo/gmclist



Foolish Carriage, 76 26' Eleganza(?) with beaucoup mods and add - ons. Braselton, Ga. I forgive them all, save those who hurt the dogs. They must answer to me in hell
Re: Honda EV4010 problem [message #137799 is a reply to message #137764] Sat, 06 August 2011 21:38 Go to previous message
Luvn737s is currently offline  Luvn737s   United States
Messages: 1106
Registered: June 2007
Karma: 2
Senior Member
I had a wild generator (Kohler) which I thought was a governor problem, but in the end was a mis-torqued cylinder head( finger-tight, actually).

Randy
1973 26' Painted Desert
Ahwatukee (Phoenix) AZ