Johnny,
It depends.
Case 1: If you have 120-volt devices on both sides of the split you will
need an adapter to feed 120-volts to both sides of your 50-amp cord. The
50-amp neutral wire becomes a weak point but the probability of you putting
more than 50-amps is quite low.
If you can move all your load to one side of your split you only need to
power one side of the 50-amp cord with an adapter but you will be limited
to 40-amps of 120-volts
Case 2: No problem. 240 volts with each side of the split the split getting
120 volts 180 degrees out of phase with each other. The neutral wire will
carry the difference current between the two busses.
On Thu, Nov 2, 2017 at 1:18 PM, Johnny Bridges via Gmclist <
gmclist@list.gmcnet.org> wrote:
> My coach has a split bus breaker box with one side of the 50A cord fed to
> each. Given there are no 240V appliances it it, doesn't matter whether it's
> plugged into 240 or 120.
>
> --johnny
>
> --
> 76 26' Eleganza(?) with beaucoup mods and add - ons.
> Braselton, Ga.
> "I forgive them all, save those who hurt the dogs. They must answer to me
> in hell" - ol Andy, paraphrased
>
>
> _______________________________________________
> GMCnet mailing list
> Unsubscribe or Change List Options:
> http://list.gmcnet.org/mailman/listinfo/gmclist_list.gmcnet.org
>
--
*John Phillips*
_______________________________________________
GMCnet mailing list
Unsubscribe or Change List Options:
http://list.gmcnet.org/mailman/listinfo/gmclist_list.gmcnet.org
Johnd01
John Phillips
Avion A2600 TZE064V101164
Rancho Cordova, CA (Sacramento)
|
|
|